Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
AKMASTER:

Per HotLine1's post:

Quote

No, the bond strap or field installed compliant conductor ONLY bonds the enclosure!

The neutral (XO) must have a compliant GEC. (Rod(s); steel;Ufer;etc.)


The Attached Drawings may be of assistance:

[Linked Image]

Fig. 1: Front View of Transformer - Details of Lead Terminations.
---------------------------------------------------------------------------------

[Linked Image]

Fig. 2: Top View of same Transformer.
a.: GEC runs out the back of the Transformer;
b.: Primary Feeders enter on the Right-Side of Transformer;
c.: Secondary Feeders exit on the Left-Side of Transformer;
d.: 3-Terminal Lug with Green Bolt (connected to XO Lug via System Bonding Jumper) is Physically Bonded to the Transformer Enclosure.
---------------------------------------------------------------------------------

[Linked Image]

Fig. 3: Transformer Winding Connections Schematic, with OCPDs and SDS Panelboard.
.......................................

Figure #3 Notes:

1.: On the Secondary side's Connections, Terminal "XO would be physically located at the "Dot" above the Green Grounding Bus.

2.: The "Ground Symbols" on the Primary and Secondary sides, are Physical Connections to the Transformer's Enclosure. These Terminations may be either a Factory-Installed Jumper, or a Field-Installed Lug.

------------------------------------------------------------
------------------------------------------------------------

These Drawings, along with many others, may be found at the Technical Reference Section of ECN.

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Scott:

As always, Thank You for the added info.

Last edited by HotLine1; 05/11/13 11:10 AM.

John
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
Any time John!!!

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Jun 2012
Posts: 75
Member
Thank you very much for your time and feedback!

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!