34
9
Greg: This is the combiner box closest to the assumed point of origin of the fire. No definitive cause or location was available as of this afternoon. That appears to be a nonmetalic combiner box with EMT. Were bonding jumpers installed? shortcircuit
shortcircuit Looks like PVC to me, I see the barcode on the bottom-most conduit.
John,
Yes please keep us informed. I would like to see the outcome of this problem was. I am still on the fence about the safety of this things.
I know I would prefer the PV systems that have the mini inverter on each PV panel. This way the DC current stops right there on the roof.
Posts: 7,383 Likes: 7
Shortcircuit: Thanks for the links!!! Appreciate it!!!
Combiner boxes are metalic, 3R, etc. conduit is PVC with grd conductor.
Documentation is being compiled on my end.
Here is another angle pic.
That looks like a Solectria combiner box.
As of Fri. there has been no root cause determined. The area of the roof has been set into a grid, the remains being tagged and boxed and removed from the roof. The remains will be reviewed further to see if a cause can be determined.
Posts: 9,935 Likes: 34
Assuming a number of the collector pans look like this.
I guess the first question I have is what happens to those collectors if they feed a bolted fault. Is there collector level over current protection? You might be looking at a symptom there and you had a bigger problem on the load side.
Greg: The combiner boxes like these are 16 circuit, finger safe fuses (midget). I'll venture a guess at 100K minimum for the fuses. I'll get the rest of the specs tommorrow.