0 members (), 183 guests, and 35 robots.
HotLine1 #208543 01/27/13 10:54 AM
Hotline...there was a fire on a roof in Bakersfield California similar to what you are showing. The cause of that fire was determined to be a groundfault. Here is a link to info on that fire...
http://nfpa.typepad.com/files/target-fire-report-09apr29.pdf
Add here is a good article by Bill Brooks...
http://www.solarabcs.org/about/publications/reports/blindspot/pdfs/BlindSpot.pdf
Your fire should be documented for the solar industry.
Where, when, and what do you know about this fire?
shortcircuit
HotLine1 #208544 01/27/13 10:58 AM
Originally Posted by HotLine1
Greg:
This is the combiner box closest to the assumed point of origin of the fire. No definitive cause or location was available as of this afternoon.
That appears to be a nonmetalic combiner box with EMT. Were bonding jumpers installed?
shortcircuit
shortcircuit #208546 01/27/13 01:35 PM
shortcircuit
Looks like PVC to me, I see the barcode on the bottom-most conduit.
HotLine1 #208548 01/27/13 01:47 PM
John,
Yes please keep us informed. I would like to see the outcome of this problem was. I am still on the fence about the safety of this things.
I know I would prefer the PV systems that have the mini inverter on each PV panel. This way the DC current stops right there on the roof.
HotLine1 #208561 01/29/13 09:03 PM
Shortcircuit:
Thanks for the links!!! Appreciate it!!!
Combiner boxes are metalic, 3R, etc. conduit is PVC with grd conductor.
Documentation is being compiled on my end.
HotLine1 #208565 01/29/13 10:27 PM
Here is another angle pic.
HotLine1 #208633 02/03/13 01:15 PM
That looks like a Solectria combiner box.
HotLine1 #208639 02/03/13 02:23 PM
As of Fri. there has been no root cause determined. The area of the roof has been set into a grid, the remains being tagged and boxed and removed from the roof. The remains will be reviewed further to see if a cause can be determined.
HotLine1 #208644 02/03/13 09:08 PM
Assuming a number of the collector pans look like this.
I guess the first question I have is what happens to those collectors if they feed a bolted fault. Is there collector level over current protection?
You might be looking at a symptom there and you had a bigger problem on the load side.
HotLine1 #208652 02/04/13 12:27 AM
Greg:
The combiner boxes like these are 16 circuit, finger safe fuses (midget). I'll venture a guess at 100K minimum for the fuses.
I'll get the rest of the specs tommorrow.