ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
From an outsider- How does tipping work?
by HotLine1 - 12/04/20 01:09 PM
Thought this was funny
by HotLine1 - 12/04/20 12:55 PM
Happy Thanksgiving
by Trumpy - 12/02/20 04:11 AM
Where is Everyone?
by Trumpy - 12/02/20 03:51 AM
What does your work place look like?
by Trumpy - 12/02/20 03:42 AM
New in the Gallery:
Facebook follies, bad wiring
FPE in Germany pt.2
Who's Online Now
0 registered members (), 16 guests, and 16 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Generators #207753 11/24/12 12:59 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
Since the storm came and went, I would like to ask a question. With the whole house generators, what do people see out there? Are the generators manufactures instructions calling for installing a ground rod at the new generator? Or no ground rod? Or are they leaving it up to the local AHJ?
Any thoughts/comments?

Work Gear for Electricians and the Trades
Re: Generators [Re: harold endean] #207754 11/24/12 01:09 PM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
Is it installed as an SDS? That may affect the answer.


Greg Fretwell
Re: Generators [Re: harold endean] #207756 11/24/12 03:20 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Typically, the instructions state ground the system per the NEC and local ordinances. It stands to reason since ground conditions vary from area to area. The local JHA determines how they are grounded

I saw a commercial from a loco poco and the flashed a resi transfer switch where all the neutrals were on the same bus. I contacted them and asking them about it and that's how they wanted wired


"Live Awesome!" - Kevin Carosa
Re: Generators [Re: harold endean] #207772 11/26/12 09:16 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
Greg,

Most generators only break both hot legs in a resi type set up, so I wouldn't call it a SDS. So then a ground rod would not be needed, right?

Re: Generators [Re: harold endean] #207773 11/26/12 09:18 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
Sparky,

All towns in NJ do not have a "Local" ordinance, We have to follow what the state adopts. For the most part the state of NJ will follow 95-99% of the NEC verbatim.

Re: Generators [Re: harold endean] #207778 11/26/12 02:05 PM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
If the generator is not an SDS, the system grounding remains the same, using the service GES. The only way you would need a ground rod was if you called it a "structure" IMHO.

250.35 still requires an equipment bonding conductor sized to 250.102(C), which tosses you back to 250.66 based on the size of the ungrounded conductors to the generator.


This does bring up an interesting conundrum. The smallest EGC in 250.66 is 8ga (but no larger than the size of the ungrounded conductors in associated rules).

#10 cable, no problem, the EGC is #10. #8 cable is a problem tho since the EGC will usually be #10.


Greg Fretwell
Re: Generators [Re: harold endean] #207851 12/02/12 12:23 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
Greg,

If you were using a generator to supply tents at a fair or something like that, Then I can see the need for a ground rod. You would then be generating your own neutral terminal at the gen. itself. At this point, I would think that the EGC would have to be a #6 cu to 2-grounding electrodes 6' apart.

Re: Generators [Re: harold endean] #207855 12/02/12 12:52 PM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
Quote

If you were using a generator to supply tents at a fair or something like that, Then I can see the need for a ground rod.



The funny thing about that idea is if you just have a portable generator running cord and plug loads, the NEC doesn't require a rod and grounding the neutral actually makes the installation more dangerous.


Greg Fretwell
Re: Generators [Re: harold endean] #207858 12/02/12 08:29 PM
Joined: Apr 2002
Posts: 7,220
HotLine1 Offline
Member
All the gens used at a golf tournament had 2 grd rods each bonded to the neutral buss at the main. These were 70KW to 2 MW units feeding everything from a 10x10 shade cover to 50kSF membrane structures.

We utilized some portable units, mostly for 120 volt power used while we were working. No ground rods for them.

I used a 6500W portable at my home for 18 days, grd from twistlock to my main panel. Backfed CB, LOTO on main CB.



John
Re: Generators [Re: harold endean] #207918 12/07/12 05:45 PM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline
Member
If the generator is not connected as a SDS, then a ground rod is not required by the NEC. I read that some county's in Florida require ground rods as a local ordinance because of all the lightning.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,220
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,248 Are you busy
206,130 Re: Forum
194,125 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3