What is a typical required light level specified for temporary general construction lighting? I have seen 50FC specified but that seems really high and had to achieve.

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
You are 5x to 10x the real rule, depending on what kind of "construction area"

it is 5 FC in general construction areas, 10 FC in batch plants and electrical equipment rooms but as low as 3 FC if you are excavating, placing concrete or storing materials

http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=STANDARDS&p_id=10630

50 FC would be a very brightly lit office.


Greg Fretwell