Temporary Construction Lighting

Posted By: cgw

Temporary Construction Lighting - 08/03/12 03:09 PM

What is a typical required light level specified for temporary general construction lighting? I have seen 50FC specified but that seems really high and had to achieve.
Posted By: gfretwell

Re: Temporary Construction Lighting - 08/03/12 04:46 PM

You are 5x to 10x the real rule, depending on what kind of "construction area"

it is 5 FC in general construction areas, 10 FC in batch plants and electrical equipment rooms but as low as 3 FC if you are excavating, placing concrete or storing materials

http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=STANDARDS&p_id=10630

50 FC would be a very brightly lit office.
Posted By: cgw

Re: Temporary Construction Lighting - 08/06/12 04:02 PM

Thanks