Outdoor dishwasher nuisance GFI tripping #206661 07/30/12 01:09 AM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline OP
Member
I have a customer (restaurant) that has an outdoor bar. It is fully-covered, but everything electrical is wired as if it is a wet location. The dishwasher is cord connected to a standard 5-20 GFI receptacle that trips fairly consistently. They replaced the entire dishwasher and the new one does the same thing.

I'd like to hard-wire the thing with a take-off box and a short piece of liquid-tight flex, but the appliance people are insistent that it remain connected via plug and receptacle.

If I have to do this, I'd like to remove the GFI receptacle from the equation by using an L5-20 "Twist Lock" receptacle and plug with an in-use cover.

Does anyone have any heartburn about doing it this way?


---Ed---

"But the guy at Home Depot said it would work."
2017 / 2014 NEC & Related Books and Study Guides
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206664 07/30/12 02:18 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
NEC prohibits your work around, AFAIK.

It's the receptacle that's probably burnt out.

They go, too, you know.

Filthy spray condenses within its workings -- presto -- you've got a troubled washer.

I'd ALWAYS replace the GFCI receptacle -- in commercial use -- when such a serious equipment swap is underway. That way the customer has a clean slate.

Last edited by Tesla; 07/30/12 02:21 AM.

Tesla
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206665 07/30/12 02:30 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
The first thing I would do is figure out why the GFCI is tripping. Do they hose this place down? Is rain blowing in?
Are there critters nesting inside the dish washer?

Otherwise you are asking, how close is it to the sink (<6'), is this a "kitchen" and is it really "outdoors"? 210.8(B) does not say NEMA 5-15, it says 15 & 20a 125v receptacle. Twist lock does not change that.


Greg Fretwell
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206666 07/30/12 10:46 AM
Joined: Mar 2004
Posts: 251
W
WESTUPLACE Offline
Member
When they replaced the dishwasher, did they use the same (old) cord. The paper in some SJ type cords will wick up moisture and cause GFCI to trip. Replace cord with an SO cable or one that has no paper filler.

Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206667 07/30/12 12:38 PM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline OP
Member
There are five GFI receptacles within reach of this dishwasher an it trips every one of them consistently. I don't see the receptacles themselves as being the culprit. Yes, it appears that they reused the original cord on the new washer, so the cord could be causing this issue. It is SO cord though. They did have their maintenance man in that morning with the power washer to clean the entire bar area, so he may have gotten a bit carried away with it.

At this point, I have told the customer to have their appliance people come out to investigate further.


---Ed---

"But the guy at Home Depot said it would work."
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206668 07/30/12 12:43 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
My bet is hosing the place down is getting water where it shouldn't be. That is common in commercial kitchens. I am not sure how you stop it.


Greg Fretwell
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206671 07/30/12 06:51 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
Ed:
Curious as to how the cord on the DW can reach the five other adjacent receptacles? 422 limits the cord to a length 3' to 4' max.

If the GFI recept is doing its intended job, then the DW or the cord is the culprit.

Removing the GFI IMHO would expose you to a liability you do not want.



John
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206679 07/31/12 10:01 AM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline OP
Member
John, there are five WP GFI receptacles all clustered together for them to use for outdoor cash registers, printers, etc. I'm in agreement with everyone though; the GFI is doing what it is supposed to do, so they will need to call in the appliance repair people. This is why they pay for their maintenance contract.


---Ed---

"But the guy at Home Depot said it would work."
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206685 07/31/12 04:10 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
This may be as simple as figuring out where the water is getting into the electrics and sealing or shielding it.


Greg Fretwell
Re: Outdoor dishwasher nuisance GFI tripping [Re: EV607797] #206692 07/31/12 09:01 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Woodhead (Molex) is the specialty player in wet receptacles/ kitchen washdown environments.

http://www.molex.com/woodhead

This situation may require abandonment of GFCI receptacles -- to be replaced by GFI circuit breakers and Woodhead washdown cord caps.

Given enough time, you can be assured that filth has invaded the inner workings of ANY GFCI receptacle on the market. They are not designed for sloppy soap/ water jets.

I'd be VERY surprised if the new equipment is the source of the trip.

BTW, there's no way the new unit has a bonding between the neutral and the grounding conductor, is there?

Last edited by Tesla; 07/31/12 09:04 PM.

Tesla

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,379
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,675 Are you busy
209,594 Re: Forum
196,946 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3