I have a customer (restaurant) that has an outdoor bar. It is fully-covered, but everything electrical is wired as if it is a wet location. The dishwasher is cord connected to a standard 5-20 GFI receptacle that trips fairly consistently. They replaced the entire dishwasher and the new one does the same thing.

I'd like to hard-wire the thing with a take-off box and a short piece of liquid-tight flex, but the appliance people are insistent that it remain connected via plug and receptacle.

If I have to do this, I'd like to remove the GFI receptacle from the equation by using an L5-20 "Twist Lock" receptacle and plug with an in-use cover.

Does anyone have any heartburn about doing it this way?