103
14
I have a situation where I need to power a intermittent single phase large load with a three phase transformer so I will not be using one leg. Its short term hook up for two to three years at best so I do not want to buy a transformer ($$$$$) when I have a 3 phase dry transformer collecting dust of sufficent size. I have not come up on this type of config before so I have my conserns. Such as
*Would it be kosher to wire and tap only two of the three coils?
*if not, what issues would I have if I were to wire the high side 3 phase and only use two legs where the amperage in theory be upto 100 amps, 90 more realistically and only intermittenly?
Posts: 7,413 Likes: 9
I've seen this done over the years, as having 3 phase wired as normal, secondaries going to a disconnect/panel, and single phase load being connected.
Can't say I heard of any problems.
IMHO, as long as the xfr is of sufficient KVA, you should be OK. Efficiency? May be an issue.
Scott....jump in here please!
Does the transformer have each end of the secondaries available for separate connection? If so, you could hook them up in a "dog leg" connection to get single phase out of a three phase source.
It is the same method that is used on three phase generators when they need to supply single phase loads.
I timed out while editting. Use the following "Scott" drawing. 12 lead generator drawings Basically it is a open delta where Phases A & B are connected in opposing series and Phase C is connected in aiding series to the combined A & B. The output "L1"is connected to the free end of A, the "neutral" is the connection between B & C, and "L2" is the free end of C. The connection between A & B is not used. This limits the unit's maximum power to 2/3 of full rating but is does load the 3 phase input equally. Larry C
I am not sure if it's a 12 wire transformer or not. I currently do not have access to it.
Larry, I think the the 12 lead generator link is hinky. It takes me to some web site. I do have schems of generators and I didn't thInk of looking at it from your perspective.
Thanx for everyone's input
Posts: 10,047 Likes: 37
Maybe I am missing something but why not terminate in a 3 pole disconnect and feed a single phase panel from there or just use a 3p panel with one 2 pole breaker plugged into it.
The transformer won't care.
That is what I'm planning to do. By maxing two of three legs while having nothing on the third leg, I dont know such an unbalance would cause any issues for the transformer and or the circuits or not. That would be a rather expensive smoke test if overlooked something
The link is hinky because address got changed from electrical-contractor .... to electrical.contractor ....
The link is supposed to go to the technical drawings on this site.
Larry
Ah ha! That did it. Thanx Larry.
Btw, I'll get the rest of my barge pics posted some day. Got super busy. Finally getting on top of things.