Transformer/engineering question #205927 04/27/12 03:49 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
I have a situation where I need to power a intermittent single phase large load with a three phase transformer so I will not be using one leg. Its short term hook up for two to three years at best so I do not want to buy a transformer ($$$$$) when I have a 3 phase dry transformer collecting dust of sufficent size. I have not come up on this type of config before so I have my conserns. Such as

*Would it be kosher to wire and tap only two of the three coils?

*if not, what issues would I have if I were to wire the high side 3 phase and only use two legs where the amperage in theory be upto 100 amps, 90 more realistically and only intermittenly?


"Live Awesome!" - Kevin Carosa
Work Gear for Electricians and the Trades
Re: Transformer/engineering question [Re: sparkyinak] #205928 04/27/12 06:45 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
I've seen this done over the years, as having 3 phase wired as normal, secondaries going to a disconnect/panel, and single phase load being connected.

Can't say I heard of any problems.

IMHO, as long as the xfr is of sufficient KVA, you should be OK. Efficiency? May be an issue.

Scott....jump in here please!


John
Re: Transformer/engineering question [Re: sparkyinak] #205931 04/28/12 01:35 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
Does the transformer have each end of the secondaries available for separate connection? If so, you could hook them up in a "dog leg" connection to get single phase out of a three phase source.

It is the same method that is used on three phase generators when they need to supply single phase loads.

Re: Transformer/engineering question [Re: LarryC] #205932 04/28/12 02:00 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
I timed out while editting. Use the following "Scott" drawing.

12 lead generator drawings

Basically it is a open delta where Phases A & B are connected in opposing series and Phase C is connected in aiding series to the combined A & B. The output "L1"is connected to the free end of A, the "neutral" is the connection between B & C, and "L2" is the free end of C. The connection between A & B is not used.

This limits the unit's maximum power to 2/3 of full rating but is does load the 3 phase input equally.

Larry C

Re: Transformer/engineering question [Re: LarryC] #205939 04/29/12 06:32 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
I am not sure if it's a 12 wire transformer or not. I currently do not have access to it.

Larry, I think the the 12 lead generator link is hinky. It takes me to some web site. I do have schems of generators and I didn't thInk of looking at it from your perspective.

Thanx for everyone's input


"Live Awesome!" - Kevin Carosa
Re: Transformer/engineering question [Re: sparkyinak] #205940 04/29/12 09:12 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Online Content
Member
Maybe I am missing something but why not terminate in a 3 pole disconnect and feed a single phase panel from there or just use a 3p panel with one 2 pole breaker plugged into it.

The transformer won't care.


Greg Fretwell
Re: Transformer/engineering question [Re: gfretwell] #205944 04/29/12 11:52 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
That is what I'm planning to do. By maxing two of three legs while having nothing on the third leg, I dont know such an unbalance would cause any issues for the transformer and or the circuits or not. That would be a rather expensive smoke test if overlooked something


"Live Awesome!" - Kevin Carosa
Re: Transformer/engineering question [Re: sparkyinak] #205947 04/30/12 11:20 AM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
The link is hinky because address got changed from electrical-contractor .... to electrical.contractor ....

The link is supposed to go to the technical drawings on this site.

Larry

Re: Transformer/engineering question [Re: LarryC] #205949 04/30/12 04:41 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
Ah ha! That did it. Thanx Larry.

Btw, I'll get the rest of my barge pics posted some day. Got super busy. Finally getting on top of things.


"Live Awesome!" - Kevin Carosa
Re: Transformer/engineering question [Re: sparkyinak] #205950 04/30/12 04:45 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
And nice drawings Scott


"Live Awesome!" - Kevin Carosa
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,648 Are you busy
209,573 Re: Forum
196,928 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3