ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,042 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#205568 03/09/12 05:18 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Dec 2000
Posts: 4,294
Member
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.

Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?

Joined: Jan 2004
Posts: 1,507
G
Member
Make sure the terminals in the Chiller are rated for 75° C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60° C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75° and #8 would be fine. The 80a. overcurrent device is proper in either case.


George Little

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5