mca and mocp nameplate #205568 03/09/12 04:18 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Re: mca and mocp nameplate [Re: Bravo] #205569 03/09/12 04:43 PM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.

Re: mca and mocp nameplate [Re: electure] #205570 03/09/12 04:49 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?

Re: mca and mocp nameplate [Re: Bravo] #205571 03/09/12 10:53 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Make sure the terminals in the Chiller are rated for 75 C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60 C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75 and #8 would be fine. The 80a. overcurrent device is proper in either case.


George Little

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,655 Are you busy
209,581 Re: Forum
196,935 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3