mca and mocp nameplate #205568
03/09/12 05:18 PM
03/09/12 05:18 PM
Bravo  Offline OP
Joined: May 2010
Posts: 30
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Re: mca and mocp nameplate [Re: Bravo] #205569
03/09/12 05:43 PM
03/09/12 05:43 PM
electure  Offline

Joined: Dec 2000
Posts: 4,265
Fullerton, CA USA
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.

Re: mca and mocp nameplate [Re: electure] #205570
03/09/12 05:49 PM
03/09/12 05:49 PM
Bravo  Offline OP
Joined: May 2010
Posts: 30
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?

Re: mca and mocp nameplate [Re: Bravo] #205571
03/09/12 11:53 PM
03/09/12 11:53 PM
George Little  Offline
Joined: Jan 2004
Posts: 1,489
Michigan USA
Make sure the terminals in the Chiller are rated for 75 C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60 C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75 and #8 would be fine. The 80a. overcurrent device is proper in either case.

George Little


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Posts: 22
Joined: August 2009