mca and mocp nameplate #205568
03/09/12 05:18 PM
03/09/12 05:18 PM
B
Bravo  Offline OP
Member
Joined: May 2010
Posts: 30
NY, USA
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Re: mca and mocp nameplate [Re: Bravo] #205569
03/09/12 05:43 PM
03/09/12 05:43 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,280
Fullerton, CA USA
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.

Re: mca and mocp nameplate [Re: electure] #205570
03/09/12 05:49 PM
03/09/12 05:49 PM
B
Bravo  Offline OP
Member
Joined: May 2010
Posts: 30
NY, USA
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?

Re: mca and mocp nameplate [Re: Bravo] #205571
03/09/12 11:53 PM
03/09/12 11:53 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,498
Michigan USA
Make sure the terminals in the Chiller are rated for 75 C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60 C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75 and #8 would be fine. The 80a. overcurrent device is proper in either case.


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
255,188 Are you busy
191,269 Re: Forum
181,026 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.007s) Memory: 0.9597 MB (Peak: 1.0942 MB) Zlib enabled. Server Time: 2019-05-24 21:05:07 UTC