ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
EMC Glands on Motors
by Trumpy - 12/01/22 06:12 AM
Ground Rods: Installation and Hook-Up
by Trumpy - 12/01/22 05:54 AM
Happy Thanksgiving all!
by gfretwell - 11/30/22 05:55 PM
Colt Firearms Switchbox
by NORCAL - 11/29/22 01:04 AM
Perfect work light?
by gfretwell - 11/22/22 12:48 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 42 guests, and 21 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#205568 03/09/12 04:18 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Dec 2000
Posts: 4,289
Member
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.

Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?

Joined: Jan 2004
Posts: 1,507
G
Member
Make sure the terminals in the Chiller are rated for 75 C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60 C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75 and #8 would be fine. The 80a. overcurrent device is proper in either case.


George Little

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 75
Joined: June 2012
Top Posters(30 Days)
Trumpy 9
NORCAL 5
Popular Topics(Views)
300,399 Are you busy
230,038 Re: Forum
214,835 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5