ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#205568 03/09/12 05:18 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2000
Posts: 4,294
Member
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.

Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?

Joined: Jan 2004
Posts: 1,507
G
Member
Make sure the terminals in the Chiller are rated for 75° C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60° C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75° and #8 would be fine. The 80a. overcurrent device is proper in either case.