ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 205 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#205541 03/02/12 05:12 PM
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
I was working on a 480v hps lighting circuit and went to turn the circuit off to change the fixture but still measured 66 volts to ground on each leg. Does. Any one know why this would be?

Joined: Jul 2004
Posts: 787
L
Member
What type of meter did you measure the voltage with? If it is an electronic meter with the high input impeadence, it will measure "ghost" voltages. These "ghost" voltages are due to the wires traveling next to energized wires. Both set of wires are acting as a transformer.

Measure the voltage with a Wiggy or equivalent and the voltage will PROBABLY disappear. If they do not disappear, you have a problem. If the voltage does disappear then you are measuring ghost voltages.

Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Measured it with a fluke multimeter.

Joined: Jun 2004
Posts: 1,273
T
Member
Fluke multimeters ARE high impedance testers.

You need to use an old-style analog meter to load down these induced voltages. Since there is no current flow, it's really a capacitive effect.



Tesla
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Cinner:

You need a 'Wiggy', or any other brand solenoid type tester, or an analog multi-meter.


John
Joined: Jul 2007
Posts: 1,335
S
Member
WIGGGGGGGY!!! I carry one in my pouch just for that


"Live Awesome!" - Kevin Carosa
Joined: Feb 2004
Posts: 1,438
Member
This happens in a cogen I work in alot.. 480V wiring from VFD loads seem to induce voltage on other conductors more than anything.. HID loaded circuits have the same tendency