C
Cinner Offline OP
Member
I was working on a 480v hps lighting circuit and went to turn the circuit off to change the fixture but still measured 66 volts to ground on each leg. Does. Any one know why this would be?

Joined: Jul 2004
Posts: 787
L
Member
What type of meter did you measure the voltage with? If it is an electronic meter with the high input impeadence, it will measure "ghost" voltages. These "ghost" voltages are due to the wires traveling next to energized wires. Both set of wires are acting as a transformer.

Measure the voltage with a Wiggy or equivalent and the voltage will PROBABLY disappear. If they do not disappear, you have a problem. If the voltage does disappear then you are measuring ghost voltages.

Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Measured it with a fluke multimeter.

Joined: Jun 2004
Posts: 1,273
T
Member
Fluke multimeters ARE high impedance testers.

You need to use an old-style analog meter to load down these induced voltages. Since there is no current flow, it's really a capacitive effect.



Tesla
Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
Cinner:

You need a 'Wiggy', or any other brand solenoid type tester, or an analog multi-meter.


John
Joined: Jul 2007
Posts: 1,335
S
Member
WIGGGGGGGY!!! I carry one in my pouch just for that


"Live Awesome!" - Kevin Carosa
Joined: Feb 2004
Posts: 1,438
Member
This happens in a cogen I work in alot.. 480V wiring from VFD loads seem to induce voltage on other conductors more than anything.. HID loaded circuits have the same tendency


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
BigB 7
triple 3
Popular Topics(Views)
302,734 Are you busy
231,965 Re: Forum
216,683 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5