hi , i have a generator that gives me 600v 3ph 120 amps and would like to have 120/208 3ph .
What size of Transformer should i use

Thanks

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
600 volts x 120 amps x 1.73 = 124,560 volt amps