#204912 01/21/12 11:12 AM
Joined: Sep 2009
Posts: 1
V
volt Offline OP
New Member
hi , i have a generator that gives me 600v 3ph 120 amps and would like to have 120/208 3ph .
What size of Transformer should i use

Thanks

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
600 volts x 120 amps x 1.73 = 124,560 volt amps

Standard transformer sizes are 112 1/2 kva (smaller) or 150 kva (larger)


Few things are harder to put up with than the annoyance of a good example.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Trumpy 5
LarryC 3
NORCAL 2
Popular Topics(Views)
291,501 Are you busy
223,930 Re: Forum
209,314 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5