Is speaker type wire 20 ga. ok for led undercab lights buried in walls? from 12v trans.

Work Gear for Electricians and the Trades
Re: Speaker wire for led under cab lights? [Re: crselectric] #204909 01/20/12 07:50 PM
Joined: Jul 2005
Posts: 57
D
distributor x Offline
Member
what variety of speaker wire? does the wire have an in-wall (FT4) rating? Run length? load?

20ga sounds extremely small


Re: Speaker wire for led under cab lights? [Re: crselectric] #204913 01/21/12 11:55 AM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
Iíd say no. Unless the low voltage wire is listed as CL2, youíre really not supposed to conceal it in the walls, etc. Thatís how it is enforced around here anyway.
The last LED kitchen lighting job I did had both in cabinet and under cabinet lighting. What I did was run the switch leg down to some J-boxes I mounted the circuit panel location in the basement and then fished a 14/2 NM up the wall to each cabinet light location from there. I mounted the drivers for them down there as well.
IMO, the benefit of using regular NM for low voltage under cabinet lighting is that you donít have to worry about the situation with concealing it in walls and also if for some reason the customer ever wants to go back to line voltage lighting, youíre all set.

Re: Speaker wire for led under cab lights? [Re: crselectric] #204926 01/22/12 12:15 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Off top of my head, with out see Mfg instructions, I would have to say no. Unless it is a complete listed and labeled for the application.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,757 Are you busy
209,666 Re: Forum
197,013 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3