400 A service entrance neutral wire size? #202625 08/15/11 06:26 PM
Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
400 A single phase 240 volt service, outside building run in 3" PVC with weatherhead.

400 A copper from 2008 Table 310.16 calls for 500 MCM THHN, but what about the size of the neutral? I've been told I can use 250 MCM, but can't seem to find a code reference.

Anybody?

Thanks!

Grov

2017 / 2014 NEC & Related Books and Study Guides
Re: 400 A service entrance neutral wire size? [Re: Grover] #202631 08/15/11 08:20 PM
Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
It appears that, since 1996 or thereabouts, the NEC "discovered" harmonics and non-linear loads, and it's been a quagmire ever since.

Re: 400 A service entrance neutral wire size? [Re: Grover] #202632 08/15/11 09:02 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
Grover:

220.61 (from '11)
"(C) Prohibited Reductions. There shall be no reduction of
the neutral or grounded conductor capacity applied to the
amount in 220.61(C)(1), or portion of the amount in (C)(2),
from that determined by the basic calculation:
(1) Any portion of a 3-wire circuit consisting of 2 ungrounded
conductors and the neutral conductor of a
4-wire, 3-phase, wye-connected system
(2) That portion consisting of nonlinear loads supplied
from a 4-wire, wye-connected, 3-phase system
Informational Note No. 1: See Examples D1(a), D1(b),
D2(b), D4(a), and D5(a) in Informative Annex D.
Informational Note No. 2: A 3-phase, 4-wire, wye-connected
power system used to supply power to nonlinear loads may
necessitate that the power system design allow for the possibility
of high harmonic neutral-conductor currents."

In addition to the above, a local POCO does NOT allow reduced neutrals for comm/ind. services that have a neutral.


John
Re: 400 A service entrance neutral wire size? [Re: Grover] #202633 08/15/11 10:23 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
If its single phase and you’re using 500 Kcmil in a single raceway, couldn’t you size your grounded/neutral conductor using 230.42[C], which references 250.24[C] in the 2011 NEC?
250.24C[1] says to use Table 250.66. Sounds crazy, but following this, it looks like 1/0 Cu would be the minimum size grounded/neutral conductor.

Re: 400 A service entrance neutral wire size? [Re: Grover] #202635 08/15/11 11:01 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
Art 250 is the grounding (earthing) article and deals with GECs and bonding conductor sizes.

Art 220 calculations allow for 'undersize' neutral conductors, based on load calculations, in some crcumstances. Usually substantial 3 phase loads, but the POCO winds up trumping the load calcs with their requirements.

IMHO, it's not $$ worth it.


John
Re: 400 A service entrance neutral wire size? [Re: HotLine1] #202637 08/15/11 11:35 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
Yes, but did they change the meaning of grounded conductor in the NEC?
230.42[C] says minimum size and rating of the grounded conductor.

It looks like what they are getting at is that if the unbalanced load calculated in 220.61 results in a ampacity of less than the conductor sized in 250.66, then that then becomes the minimum size for the grounded service conductor. In essense it appears they are saying that the grounded/neutral conductor can't be smaller than the grounding conductor.

Re: 400 A service entrance neutral wire size? [Re: Grover] #202638 08/16/11 12:14 AM
Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
Thanks for all the comments guys! I'll dig some more, but, as I said before, it's a single phase 240 V system, not 3 phase, and it's a small variety store with pizza ovens etc, and we're still on the 2008 code back here in the woods!

Grov

Re: 400 A service entrance neutral wire size? [Re: Grover] #202639 08/16/11 01:28 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
PG&E routinely uses undersized neutrals:

1000 KCmil hots (3)
350 KCmil neutral (1)
no ground bond
3 phase system.
per pipe... each 5" (EUSERC) last job only 3 out of 8 pipes had wire.
The MAIN was set at 2,000 Amps
This enters a EUSERC big box from below slab... with dependent Services at 400, 400, and a string of 200's

-------

I've installed 3 phase panels with massive 3 phase rotary loads.
1100 Amps in a 1200 Frame chassis -- four raceways with a massive Al bonding wire ( 1100 Amps ) while the largest possible unbalanced load was 90A resulting in a dinky neutral.

Reducing the Service neutral is entirely determined by the Poco -- it's outside the scope of the NEC. That hunk of wire is going to be deeded over to the Poco and become their liability for performance.

Because of those dynamics, it's almost never worth the hassle of even raising the topic -- unless it's been established on the approved one-line submitted at the beginning.

The answer to this issue is never to be found in the NEC. It's a Poco thing. They have their standards -- and they don't give a dang what the NEC says.


Tesla
Re: 400 A service entrance neutral wire size? [Re: Grover] #202640 08/16/11 05:04 AM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
FYI, in BC we have a directive that provides interpretation about the neutral derating that is permitted under certain circumstances under Canadian Code. The rule recognizes effects of third harmonics from specific loads.

http://safetyauthority.ca/sites/def...4%20Section%204%20-%20Conductors%202.pdf

Re: 400 A service entrance neutral wire size? [Re: Grover] #202647 08/16/11 02:28 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
Grover:
NJ is still '08 NEC as of today, just FYI.

The main reasoning for NOT undersizing the neutral is what happens upon a change of occupancy/use of the structure.

As I said, IMHO, it's not worth the brain cells, and BTW, what is your POCO requirements? Also, have you ran this by the local AHJ?



John
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,506 Are you busy
194,890 Re: Forum
184,329 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3