400 A service entrance neutral wire size? #202625
08/15/11 05:26 PM
08/15/11 05:26 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
400 A single phase 240 volt service, outside building run in 3" PVC with weatherhead.

400 A copper from 2008 Table 310.16 calls for 500 MCM THHN, but what about the size of the neutral? I've been told I can use 250 MCM, but can't seem to find a code reference.

Anybody?

Thanks!

Grov

2017 / 2014 NEC & Related Books and Study Guides
Re: 400 A service entrance neutral wire size? [Re: Grover] #202631
08/15/11 07:20 PM
08/15/11 07:20 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
It appears that, since 1996 or thereabouts, the NEC "discovered" harmonics and non-linear loads, and it's been a quagmire ever since.

Re: 400 A service entrance neutral wire size? [Re: Grover] #202632
08/15/11 08:02 PM
08/15/11 08:02 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
Grover:

220.61 (from '11)
"(C) Prohibited Reductions. There shall be no reduction of
the neutral or grounded conductor capacity applied to the
amount in 220.61(C)(1), or portion of the amount in (C)(2),
from that determined by the basic calculation:
(1) Any portion of a 3-wire circuit consisting of 2 ungrounded
conductors and the neutral conductor of a
4-wire, 3-phase, wye-connected system
(2) That portion consisting of nonlinear loads supplied
from a 4-wire, wye-connected, 3-phase system
Informational Note No. 1: See Examples D1(a), D1(b),
D2(b), D4(a), and D5(a) in Informative Annex D.
Informational Note No. 2: A 3-phase, 4-wire, wye-connected
power system used to supply power to nonlinear loads may
necessitate that the power system design allow for the possibility
of high harmonic neutral-conductor currents."

In addition to the above, a local POCO does NOT allow reduced neutrals for comm/ind. services that have a neutral.


John
Re: 400 A service entrance neutral wire size? [Re: Grover] #202633
08/15/11 09:23 PM
08/15/11 09:23 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
If its single phase and you’re using 500 Kcmil in a single raceway, couldn’t you size your grounded/neutral conductor using 230.42[C], which references 250.24[C] in the 2011 NEC?
250.24C[1] says to use Table 250.66. Sounds crazy, but following this, it looks like 1/0 Cu would be the minimum size grounded/neutral conductor.

Re: 400 A service entrance neutral wire size? [Re: Grover] #202635
08/15/11 10:01 PM
08/15/11 10:01 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
Art 250 is the grounding (earthing) article and deals with GECs and bonding conductor sizes.

Art 220 calculations allow for 'undersize' neutral conductors, based on load calculations, in some crcumstances. Usually substantial 3 phase loads, but the POCO winds up trumping the load calcs with their requirements.

IMHO, it's not $$ worth it.


John
Re: 400 A service entrance neutral wire size? [Re: HotLine1] #202637
08/15/11 10:35 PM
08/15/11 10:35 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Yes, but did they change the meaning of grounded conductor in the NEC?
230.42[C] says minimum size and rating of the grounded conductor.

It looks like what they are getting at is that if the unbalanced load calculated in 220.61 results in a ampacity of less than the conductor sized in 250.66, then that then becomes the minimum size for the grounded service conductor. In essense it appears they are saying that the grounded/neutral conductor can't be smaller than the grounding conductor.

Re: 400 A service entrance neutral wire size? [Re: Grover] #202638
08/15/11 11:14 PM
08/15/11 11:14 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
Thanks for all the comments guys! I'll dig some more, but, as I said before, it's a single phase 240 V system, not 3 phase, and it's a small variety store with pizza ovens etc, and we're still on the 2008 code back here in the woods!

Grov

Re: 400 A service entrance neutral wire size? [Re: Grover] #202639
08/16/11 12:28 AM
08/16/11 12:28 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
PG&E routinely uses undersized neutrals:

1000 KCmil hots (3)
350 KCmil neutral (1)
no ground bond
3 phase system.
per pipe... each 5" (EUSERC) last job only 3 out of 8 pipes had wire.
The MAIN was set at 2,000 Amps
This enters a EUSERC big box from below slab... with dependent Services at 400, 400, and a string of 200's

-------

I've installed 3 phase panels with massive 3 phase rotary loads.
1100 Amps in a 1200 Frame chassis -- four raceways with a massive Al bonding wire ( 1100 Amps ) while the largest possible unbalanced load was 90A resulting in a dinky neutral.

Reducing the Service neutral is entirely determined by the Poco -- it's outside the scope of the NEC. That hunk of wire is going to be deeded over to the Poco and become their liability for performance.

Because of those dynamics, it's almost never worth the hassle of even raising the topic -- unless it's been established on the approved one-line submitted at the beginning.

The answer to this issue is never to be found in the NEC. It's a Poco thing. They have their standards -- and they don't give a dang what the NEC says.


Tesla
Re: 400 A service entrance neutral wire size? [Re: Grover] #202640
08/16/11 04:04 AM
08/16/11 04:04 AM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
FYI, in BC we have a directive that provides interpretation about the neutral derating that is permitted under certain circumstances under Canadian Code. The rule recognizes effects of third harmonics from specific loads.

http://safetyauthority.ca/sites/def...4%20Section%204%20-%20Conductors%202.pdf

Re: 400 A service entrance neutral wire size? [Re: Grover] #202647
08/16/11 01:28 PM
08/16/11 01:28 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
Grover:
NJ is still '08 NEC as of today, just FYI.

The main reasoning for NOT undersizing the neutral is what happens upon a change of occupancy/use of the structure.

As I said, IMHO, it's not worth the brain cells, and BTW, what is your POCO requirements? Also, have you ran this by the local AHJ?



John
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,195 Are you busy
189,176 Re: Forum
178,850 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 16 (0.006s) Memory: 1.0296 MB (Peak: 1.2114 MB) Zlib enabled. Server Time: 2018-12-14 01:46:22 UTC