0 members (), 163 guests, and 11 robots.
#201369 05/29/11 11:03 PM
MJ2000 Offline OP
Hi,
Is it allowed to make joints in LB fittings?
MJ
MJ2000 #201372 05/29/11 11:25 PM
I could be wrong,but I think as long as it meets the cu in box fill requirement It may be allowed.I would never splice service conductors though.
between meter and service disconnect that is. smile
MJ2000 #201374 05/29/11 11:40 PM
I think it is something to be avoided. There is no provision for bonding in an LB, it is difficult to maintain 150mm of conductors for splicing, and some may consider an LB to be a raceway, and we know joints are not permitted within raceways.That being said I dont think there is a rule that specifically prohibits splicing in an LB.
MJ2000 #201414 05/31/11 07:24 PM
If the conduit body has a cubic inch area marked on it then you can splice in it according to 12-3034
mikesh #201443 06/01/11 12:22 PM
My reading of 12-3034 is that it refers to boxes, whereas an LB would be considered a fitting - so should 12-3034 apply?
MJ2000 #201449 06/01/11 07:26 PM
Just a little insight from the NEC Standpoint:
314.16 (c) 2011 NEC
(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner.
IMHO, splicing within an LB, LL, LR, C, T, etc. is not a respected trade practice, and not often seen.