LB Fittings #201369 05/29/11 10:03 PM
Joined: Jun 2005
Posts: 17
M
MJ2000 Offline OP
Member
Hi,
Is it allowed to make joints in LB fittings?

MJ

Tools for Electricians:
Re: LB Fittings [Re: MJ2000] #201372 05/29/11 10:25 PM
Joined: May 2003
Posts: 1,155
dougwells Offline
Member
I could be wrong,but I think as long as it meets the cu in box fill requirement It may be allowed.I would never splice service conductors though.
between meter and service disconnect that is. smile

Re: LB Fittings [Re: MJ2000] #201374 05/29/11 10:40 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
I think it is something to be avoided. There is no provision for bonding in an LB, it is difficult to maintain 150mm of conductors for splicing, and some may consider an LB to be a raceway, and we know joints are not permitted within raceways.That being said I dont think there is a rule that specifically prohibits splicing in an LB.

Re: LB Fittings [Re: MJ2000] #201414 05/31/11 06:24 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
If the conduit body has a cubic inch area marked on it then you can splice in it according to 12-3034

Re: LB Fittings [Re: mikesh] #201443 06/01/11 11:22 AM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
My reading of 12-3034 is that it refers to boxes, whereas an LB would be considered a fitting - so should 12-3034 apply?

Re: LB Fittings [Re: MJ2000] #201449 06/01/11 06:26 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
Just a little insight from the NEC Standpoint:

314.16 (c) 2011 NEC

(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner.

IMHO, splicing within an LB, LL, LR, C, T, etc. is not a respected trade practice, and not often seen.



John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,722 Are you busy
209,640 Re: Forum
196,985 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3