LB Fittings
#201369
05/29/11 10:03 PM
|
Joined: Jun 2005
Posts: 17
OP
Member
|
Hi, Is it allowed to make joints in LB fittings?
MJ
|
|
|
Re: LB Fittings
[Re: MJ2000]
#201372
05/29/11 10:25 PM
|
Joined: May 2003
Posts: 1,155
Member
|
I could be wrong,but I think as long as it meets the cu in box fill requirement It may be allowed.I would never splice service conductors though. between meter and service disconnect that is. 
|
|
|
Re: LB Fittings
[Re: MJ2000]
#201374
05/29/11 10:40 PM
|
Joined: Jul 2005
Posts: 183
Member
|
I think it is something to be avoided. There is no provision for bonding in an LB, it is difficult to maintain 150mm of conductors for splicing, and some may consider an LB to be a raceway, and we know joints are not permitted within raceways.That being said I dont think there is a rule that specifically prohibits splicing in an LB.
|
|
|
Re: LB Fittings
[Re: MJ2000]
#201414
05/31/11 06:24 PM
|
Joined: Jun 2006
Posts: 613
Member
|
If the conduit body has a cubic inch area marked on it then you can splice in it according to 12-3034
|
|
|
Re: LB Fittings
[Re: mikesh]
#201443
06/01/11 11:22 AM
|
Joined: Jul 2005
Posts: 183
Member
|
My reading of 12-3034 is that it refers to boxes, whereas an LB would be considered a fitting - so should 12-3034 apply?
|
|
|
Re: LB Fittings
[Re: MJ2000]
#201449
06/01/11 06:26 PM
|
Joined: Apr 2002
Posts: 7,235
Member
|
Just a little insight from the NEC Standpoint:
314.16 (c) 2011 NEC
(2) With Splices, Taps, or Devices. Only those conduit bodies that are durably and legibly marked by the manufacturer with their volume shall be permitted to contain splices, taps, or devices. The maximum number of conductors shall be calculated in accordance with 314.16(B). Conduit bodies shall be supported in a rigid and secure manner.
IMHO, splicing within an LB, LL, LR, C, T, etc. is not a respected trade practice, and not often seen.
John
|
|
|
|
|