bonding jumper or GEC #200530
04/06/11 12:26 AM
04/06/11 12:26 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
A GEC from the panel terminates to the water pipe, then a bonding jumper from the water pipe terminates on the ground rod.
One of my colleague says it is a violation because it has to be one continuous piece from the panel to the water pipe then to the ground rod.

I say the only portion that has to be continuous is the GEC not the bonding jumper that is to the ground rod.

i will try to post the picture.




Last edited by Niko; 04/06/11 12:37 AM.

Be kind to your neighbor, he knows where you live

2017 / 2014 NEC & Related Books and Study Guides
Re: bonding jumper or GEC [Re: Niko] #200538
04/06/11 09:26 AM
04/06/11 09:26 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
The GEC need only be continuous between the panel and the first grounding electrode.

Code language can lead you to your friends' view, but the matter is addressed in Soares. Call it another example of bad grammar on the part of the NEC.

Re: bonding jumper or GEC [Re: Niko] #200541
04/06/11 09:52 AM
04/06/11 09:52 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Reno,

Another section of "Bad Grammar" in the NEC IMHO is under 680 for "Bonding". Where the bonding conductor must be "Continuous without splice", but you can land 2 pieces of bonding wire under a proper bonding lug strip. Like in a deck box, you have the #8 from the light into a bonding lug, and on another bonding lug you have the #16 ground wire from the light and the #12 grounding wire from the circuit that feeds the light.

Re: bonding jumper or GEC [Re: Niko] #200546
04/06/11 10:30 AM
04/06/11 10:30 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 935
Chicago Illinois USA
A lot of the lugs that I see for conduits and pipes are designed so that you can lay the conductor in the lug and tighten it without having to cut the wire.


Ghost307
Re: bonding jumper or GEC [Re: Niko] #200548
04/06/11 01:51 PM
04/06/11 01:51 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Ghost,

I have seen those kinds of bonding bushings too. They are fine and acceptable. I was referring in my post about using approved lugs to connect "Bond" wires to and yet it doesn't mean "Without Splice". Some EC's go to great extent to run wires without splice but fail to use these lugs that are approved for use.

Re: bonding jumper or GEC [Re: Niko] #200559
04/06/11 11:04 PM
04/06/11 11:04 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
My only problem with landing on the rod first is what size wire is that? wink


Greg Fretwell
Re: bonding jumper or GEC [Re: gfretwell] #200562
04/07/11 02:48 AM
04/07/11 02:48 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Originally Posted by gfretwell
My only problem with landing on the rod first is what size wire is that? wink


it is #4 to the water pipe first then a separate piece of #4 goes to the ground rod.

How can i post a picture?

Last edited by Niko; 04/07/11 02:51 AM.

Be kind to your neighbor, he knows where you live

Re: bonding jumper or GEC [Re: Niko] #200568
04/07/11 06:50 PM
04/07/11 06:50 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
That is exactly right the way you described it in the OP.
I thought I heard you went to the rod first, Even then it would be OK as long as you had the #4 or whatever 250.66 calls (to bond the water pipe)
The GEC is the first connection to an electrode. everything is a bonding jumper.

From the handbook

[Linked Image]


Greg Fretwell
Re: bonding jumper or GEC [Re: gfretwell] #200575
04/08/11 04:02 AM
04/08/11 04:02 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Thank you Greg, That is exactly what the installation is.
i have that picture in my hand book i have been trying to post a picture of the installation.


Be kind to your neighbor, he knows where you live

Re: bonding jumper or GEC [Re: Niko] #200579
04/08/11 09:02 AM
04/08/11 09:02 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
This is from the FAQ

Quote

When creating a new thread or response, you'll see a "File Manager" link on the "Full Reply" or "New Post" page. When selecting this option you'll receive a popup which will allow you to attach files to your post.

Steps:
1. Click "File Manager" to bring up the "Attachment" window.
2. Click "Browse" to bring up the file browser window; this will allow you to browse your computer for any files or images you wish to upload; please note that you're bound by whatever the "allowed file type" setting is for the board.
3. Click "open" on the file you wish to upload.
4. Enter a description of what the file is (if you want to).
5. Click "add file" to add another file, or "done" to close the window and complete your posting.

Please note that you must enter some text in both the "subject" and "post" fields when responding otherwise you will receive an error; you cannot just respond with an attachment wink.



I put the photos I post on my web page and link them with the UBB "img" command.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,868 Are you busy
182,918 Re: Forum
172,743 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.038s Queries: 16 (0.006s) Memory: 1.0270 MB (Peak: 1.2087 MB) Zlib enabled. Server Time: 2018-04-22 06:50:19 UTC