#198811 - 02/05/11 12:26 AM Mix of Conductors  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
In the same conduit are you allowed to run normal 60hz and also 50hz conductors? as long as they are marked? There is a conduit that was run for equipment that has controls of 50hz. We want to pull #10's through the same conduit for a small water heater, which will be 60hz.
Thanks - SJT


2017 / 2014 NEC & Related Books and Study Guides

#198816 - 02/05/11 04:42 AM Re: Mix of Conductors [Re: SJT]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
I don't think the NEC even talks about line frequency. As long as they are all chapter 3 wiring methods below 600v I think they can live together.


Greg Fretwell

#198819 - 02/05/11 10:56 AM Re: Mix of Conductors [Re: gfretwell]  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
Thanks Greg, Going through the existing conduit would save alot of Labor and material.


#198823 - 02/05/11 02:34 PM Re: Mix of Conductors [Re: SJT]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
Derating might be an issue


Greg Fretwell

#198824 - 02/05/11 02:37 PM Re: Mix of Conductors [Re: SJT]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Not a code issue but a operational check.

When the water heater elements switch on and off, will the induced voltages interfere with the 50 Hz controls?

Larry C


#198853 - 02/06/11 12:27 AM Re: Mix of Conductors [Re: LarryC]  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
Good Point,
I'm not sure how the two HZ's would react. I'd rather not go that route if there is a possible problem. Could a wire with a different HZ induce something onto the other conductors? I guess that is the question.
SJT


#198862 - 02/06/11 03:12 AM Re: Mix of Conductors [Re: SJT]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
I don't see a problem. If you think so, twist the wires a few times.


Greg Fretwell

#198865 - 02/06/11 08:36 AM Re: Mix of Conductors [Re: SJT]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
I am not as concerned about the difference in frequency, it is more of a concern about how sensitive the 50 Hz CONTROL lines are.

The controls are are relays and lamps, no big deal. If the controls lines are for frequency meters or high impeadance sensors, then yes, it could be a big deal.

Are the control wires shielded? Do you know what type of signals are on these wires?


#198891 - 02/07/11 10:42 AM Re: Mix of Conductors [Re: SJT]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
My old boss use to work in a big factory here in northern NJ and they use to have many different frequency lines. ( I believe they did a lot of work for satellites)What they would do is make sure that the odd frequency wires were marked and labeled with different colors. (Like purple) This way they didn't get the 120/240 red, blue, black and the 277/480 Brown, orange, yellow mixed up with the 500 Hz which was purple.



Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.022s Queries: 15 (0.004s) Memory: 0.8015 MB (Peak: 0.9726 MB) Zlib enabled. Server Time: 2017-10-18 11:09:28 UTC