#198802 - 02/04/11 10:50 PM minimum OCPD for wall oven  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Here is the info given in the installation instruction from the oven manufacturer.

7200W, 240V dedicated 30Amp circuit

I know the minimum is 30A OCPD with # minimum #10 conductors.

Now for the maximum i figured 40Amps OCPD according to 422.11(E)(3)
30 x 150% = 37.5Amps

Am i correct on this?


Be kind to your neighbor, he knows where you live


2017 / 2014 NEC & Related Books and Study Guides

#198810 - 02/05/11 12:03 AM Re: minimum OCPD for wall oven [Re: Niko]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Niko:
30 x 150% equates to 45 . 37.5 would equate to 125% of 30.

Math aside, some may interpert the nameplate as "30 amp max", as I read it....dedicated 30 amp circuit.







John

#198818 - 02/05/11 05:34 AM Re: minimum OCPD for wall oven [Re: Niko]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
But if one doesn't interpret the name plate as the MAX, then one can use 30 x 150% and install a maximum 45A OCPD?

Thanks



Be kind to your neighbor, he knows where you live


#198821 - 02/05/11 11:31 AM Re: minimum OCPD for wall oven [Re: Niko]  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
Niko,
If I had to run a circuit to the oven, I would run #8's. If the oven draws 30 amps on full (Thanksgiving Dinner) then your wire size needs to be 8's onto a 40 amp Breaker. (4 wire)
Good Day



Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.7611 MB (Peak: 0.8931 MB) Zlib enabled. Server Time: 2017-10-23 22:43:37 UTC