minimum OCPD for wall oven #198802
02/04/11 09:50 PM
02/04/11 09:50 PM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Here is the info given in the installation instruction from the oven manufacturer.

7200W, 240V dedicated 30Amp circuit

I know the minimum is 30A OCPD with # minimum #10 conductors.

Now for the maximum i figured 40Amps OCPD according to 422.11(E)(3)
30 x 150% = 37.5Amps

Am i correct on this?


Be kind to your neighbor, he knows where you live

2017 / 2014 NEC & Related Books and Study Guides
Re: minimum OCPD for wall oven [Re: Niko] #198810
02/04/11 11:03 PM
02/04/11 11:03 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,069
Brick, NJ USA
Niko:
30 x 150% equates to 45 . 37.5 would equate to 125% of 30.

Math aside, some may interpert the nameplate as "30 amp max", as I read it....dedicated 30 amp circuit.







John
Re: minimum OCPD for wall oven [Re: Niko] #198818
02/05/11 04:34 AM
02/05/11 04:34 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
But if one doesn't interpret the name plate as the MAX, then one can use 30 x 150% and install a maximum 45A OCPD?

Thanks



Be kind to your neighbor, he knows where you live

Re: minimum OCPD for wall oven [Re: Niko] #198821
02/05/11 10:31 AM
02/05/11 10:31 AM
S
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
Niko,
If I had to run a circuit to the oven, I would run #8's. If the oven draws 30 amps on full (Thanksgiving Dinner) then your wire size needs to be 8's onto a 40 amp Breaker. (4 wire)
Good Day


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,260
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
andey 3
Popular Topics(Views)
253,236 Are you busy
189,883 Re: Forum
179,588 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.036s Queries: 15 (0.005s) Memory: 0.9597 MB (Peak: 1.0927 MB) Zlib enabled. Server Time: 2019-02-18 20:41:38 UTC