Posted By: Niko minimum OCPD for wall oven - 02/05/11 02:50 AM
Here is the info given in the installation instruction from the oven manufacturer.

7200W, 240V dedicated 30Amp circuit

I know the minimum is 30A OCPD with # minimum #10 conductors.

Now for the maximum i figured 40Amps OCPD according to 422.11(E)(3)
30 x 150% = 37.5Amps

Am i correct on this?
Posted By: HotLine1 Re: minimum OCPD for wall oven - 02/05/11 04:03 AM
Niko:
30 x 150% equates to 45 . 37.5 would equate to 125% of 30.

Math aside, some may interpert the nameplate as "30 amp max", as I read it....dedicated 30 amp circuit.





Posted By: Niko Re: minimum OCPD for wall oven - 02/05/11 09:34 AM
But if one doesn't interpret the name plate as the MAX, then one can use 30 x 150% and install a maximum 45A OCPD?

Thanks

Posted By: SJT Re: minimum OCPD for wall oven - 02/05/11 03:31 PM
Niko,
If I had to run a circuit to the oven, I would run #8's. If the oven draws 30 amps on full (Thanksgiving Dinner) then your wire size needs to be 8's onto a 40 amp Breaker. (4 wire)
Good Day