ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Furnace igniter leaking noise to stereo
by sparkyinak. 05/20/18 07:20 PM
turning down possible problem customer
by gfretwell. 05/19/18 07:31 PM
electircal ageing test on IPC
by HotLine1. 05/14/18 09:42 AM
What estimating software do you recommend?
by wattsittoyou. 05/14/18 06:28 AM
Rolling Scaffold - what do you do?
by HotLine1. 05/11/18 09:05 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
1 registered members (sparkyinak), 7 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
lightning protection conductor #198336
01/18/11 11:41 PM
01/18/11 11:41 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
The lightning protection wire is run inside pvc through the building I am working on. However, a 50' stretch is run outside the pvc and simply strapped-up to the steel decking through the ceiling of one room. Surely this cannot be allowed? In the event of a lightning strike, couldn't the arcing and sparking created between the wire and the deck result in a fire?

2017 / 2014 NEC & Related Books and Study Guides
Re: lightning protection conductor [Re: triple] #198340
01/19/11 01:41 AM
01/19/11 01:41 AM
G
georgestolz  Offline
Member
Joined: Jun 2005
Posts: 91
Fort Collins, CO, US
I can't think of an NEC violation, but it might run against the... NFPA 780? Whatever the lightning one is.


-George
Re: lightning protection conductor [Re: georgestolz] #198347
01/19/11 10:40 AM
01/19/11 10:40 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,963
Brick, NJ USA
Lightning protection here (NJ) are installed by "Certified Installers" to the best of my knowledge. As an EC, the sites that I worked on (Country Clubs) had a lightning contractor.

What you described does not sound 'right', but that's just a off the cuff comment. All the conductors that I have noticed were routed on the exteriors of the structures.



John
Re: lightning protection conductor [Re: HotLine1] #198505
01/24/11 02:27 PM
01/24/11 02:27 PM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
Just some items to be aware of besides the certified installer.

There is no typical requirement stating that the "down conductors" not allowed being run through the interior of a building. That being said, it does create alot more bonding issues that must be taken care of (flashovers).

There is no normal installation "shall" requirement that the conductors be in conduit.

But simply strapping a down conductor to steel decking does not meet bonding requirements assuming strapping means something to just hold the condutors in place (every 36" maximum). These are typically bonded via bonding plates or cadwelded. Whatever is used it is listed for lightning protection and has very specific requirements.

There are however requirements for regular yearly inspection of the system.

I am sorry that I can't put more information into this reply, but that would involve teaching a course on lightning protection.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,845 Are you busy
184,205 Re: Forum
173,446 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9603 MB (Peak: 1.0949 MB) Zlib enabled. Server Time: 2018-05-21 01:14:05 UTC