#198335 01/18/11 11:12 PM
Joined: Apr 2002
Posts: 203
T
triple Offline OP
Member
Does a 1/2" copper condensate line mounted to the floor 3'3" back from the front of a 277/480V VFD violate condition 2 in table 110.26(A)(1)? This pipe (grounded part) is something that could get stepped on but not backed-into like a steel railing or concrete wall so why should it be seen any different than the concrete an electrician would be standing on? If it is a violation then apparently a ridge or step in the concrete floor (even one only a fraction of an inch high) at 3'3" back would also be against the NEC.

Work Gear for Electricians and the Trades

Workgear for Electricians

triple #198855 02/06/11 12:44 AM
Joined: Jul 2002
Posts: 241
S
SJT Offline
Member
Triple,
The 3'3" is close to the 3'6" needed to satisfy the code. If the AHJ is saying it is in violation, could the condensate pipe be moved back, to keep peace?
SJT

triple #198890 02/07/11 10:38 AM
Joined: Feb 2002
Posts: 2,233
H
Member
You could have them encase the cooper line in concrete but that might be a little too severe.