11,500 foot run of 10/4 AWG wire?? #197837
12/23/10 12:44 AM
12/23/10 12:44 AM
B
Bigplanz  Offline OP
Member
Joined: Mar 2009
Posts: 73
Louisville, Kentucky
I must be missing something, but I've never heard of a two mile run of 10 gauge wire. A lot went wrong with this install, but two miles of 10 gauge wire?!?!? Help me out here, am I reading this right?

The report mentions that line voltage was maintained with transformers, but what I have never heard of was that long of a run, in re: resistance.

"In order to maintain line voltage, two Acme Electrical Corporation boosting transformers were inserted in the circuit at six separate locations. Placement was determined by the drop in line voltage from 480 VAC down to 440 VAC, phase to phase."

Is this unusual in an industrial setting?

Mining accident report


Last edited by Bigplanz; 12/23/10 12:50 AM. Reason: clarify question, add info.
Arc Flash PPE Clothing, LOTO & Insulated Tools
Re: 11,500 foot run of 10/4 AWG wire?? [Re: Bigplanz] #197844
12/23/10 11:20 AM
12/23/10 11:20 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
It's not an industrial setting - it's a mining operation. Mining operates under a different set of rules. I don't know them, so I can't comment

From my 'gut feeling,' 60 amps seems a lot for #10, and I never have liked 480 or 240v "two hots" circuits.

Oddly enough, the GEMS data would have revealed this problem- at the end of the line, a direct short to the ground wire would not draw enough power to trip the breaker. I'll bet the lights weren't working that well.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,403 Are you busy
188,015 Re: Forum
177,583 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9462 MB (Peak: 1.0601 MB) Zlib enabled. Server Time: 2018-10-19 01:10:23 UTC