Providing a CT has the amperage output, can a single CT provide accurate signalling to two or more meters requiring a CT?


"Live Awesome!" - Kevin Carosa
sparkyinak #197202 11/14/10 05:45 PM
Joined: Jul 2004
Posts: 787
L
Member
I will take a wild guess, but if the two meters are physically close AND you connect the two meter's CT inputs in SERIES, I think yes.

Acceptable practice, I do not know.

LarryC #197207 11/14/10 08:16 PM
Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
Another wild guess of 'yes'. Pondering a little deeper, I would venture a guess that as long as the 'meter' device doesn't exceed the power (correct term?) output of the CT, multiple 'meters' could be attached.


John
HotLine1 #197215 11/14/10 11:11 PM
Joined: Jul 2007
Posts: 1,335
S
Member
It makes sense to me, but would degrade the accuracy is what I'm concern.


"Live Awesome!" - Kevin Carosa
sparkyinak #197216 11/15/10 12:20 AM
Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
My guess is the manufacturer will not guarantee the accuracy if it is not installed exactly the way they say.


Greg Fretwell
gfretwell #197225 11/15/10 09:07 AM
Joined: Nov 2000
Posts: 2,148
R
Member
CTs have a rated maximum current output and a maximum circuit resistance. As long as the load of the multiple meters is below the maximum permitted load, there will be no issues with the operation or accuracy.
http://www.nktechnologies.com/pdfs/ct-tutorial.pdf


Don(resqcapt19)
resqcapt19 #197234 11/15/10 01:54 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
In the days of electromechanical meters it was standard practice to provide a single set of CT's to feed both the Ammeter and the Wattmeter. Even in today's world of electronic meters it is still common.

However, it is rare that a protective device and a meter will share a single set of CT's (although it seems common in MV starter applications).


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,482 Are you busy
231,875 Re: Forum
216,499 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5