C
Member
Can I use sealtite in multi family dwelling in outside well covered area to run feeders to third floor, emt would have to be installed in 26 inch sections due to changes in floor framing at stairway decks, its passing thru storage cabinets and floors. original plan was to pass long sections up from basement, but went awry. it would be about 45 foot run, then emt in side apartment.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
LFMC?
Yes as long as you properly secure it and you can say it is not subject to physical damage.
You also need to pull a grounding conductor in the raceway since it is more than 6'
LFNC "carflex" has similar rules once you wade through the references.


Greg Fretwell
Joined: Jun 2004
Posts: 1,273
T
Member
Actually tugging in feeders, considering the bends, will be tougher than you expect. I'd lay on the lube and upsize the raceway one bump. Further, I'd really work on my strapping scheme at every direction change. Lastly, I'd make up my pulling head with extra special care.

You might well consider getting MC - coated? - suitable for exterior use.

If it needs a beauty sheath after the fact that's not so bad. Otherwise, a mere paint job could make the MC blend in. While hefting MC may seem tough, going to Aluminum feeder conductors really cuts weight.


Tesla
Joined: Sep 2006
Posts: 155
C
Member
my question was more about fire rating and whether pvc jacketed flex was disallowed in bldg over three floors. So I ended up using steel flex and will have to beautify the exposed portions, the customer doesnt like ropey look, maybe walker duct makes covers I could use.I've seen them used to cover multiple coax runs

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I know of no building height limits on LFMC


Greg Fretwell