Gas and hydro in a trench #194785 06/22/10 03:19 PM
Joined: Dec 2005
Posts: 12
O
Oh Well Offline OP
Member
To supply an inground pool I want to install water, hydro and gas in the same trench which will be 24 in. deep. The PVC for the hydro will be at 18 in. but what about the other two. Possibly the gas at the bottom which would be 6 in. from the hydro. Thanks in advance

Tools for Electricians:
Re: Gas and hydro in a trench [Re: Oh Well] #194786 06/22/10 04:09 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline
Member
I am going to guess you are one of our neighbors to the North( canadian). In my neck of the woods, Souteastern USA this would not be a problem, with at least 6 inches of fill between each, I would still talk with each utility and get their blessing on the project. If it were my project the trench would be 30 inches deep, electric on the bottom, 6 inches of fill then gas, 6 inches of fill then water, this would give the water pipe about 16 inches of cover, plenty in my area to prevent freezing. This arrangement also means that any one who accidentily digs in to this area is likely to hit the water line first and maybe stop digging before te gas or power is cut.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Gas and hydro in a trench [Re: wire_twister] #194795 06/22/10 08:44 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
'Stacked' electric, gas, & water is definitely not a good design decission. Common install is electric and gas in the bottom of the trench, with a minimum 6" seperation. Trench depth is 24" min. Water is not a common item in pool trenching.

BTW, the above are not 'utility company' jurisdiction here, jurisdiction is Building Dept.


John
Re: Gas and hydro in a trench [Re: HotLine1] #194798 06/22/10 09:07 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline
Member
Hot Line
The utility does not have jurisdiction here either, but in the land of electric co-ops, and propane tanks, it helps to do anything you can to promote good relationships with the local utility companies, just makes things easier.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Gas and hydro in a trench [Re: Oh Well] #194863 06/28/10 12:40 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
Your direction for the electrical component of course comes from 12-012 and table 53, but the other systems you have to refer also to gas and plumbing codes. I could not find anything in the CEC that discusses separation from those systems.

Re: Gas and hydro in a trench [Re: jay8] #194908 06/29/10 07:49 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
See rule 12-012 (13)
It refers to CSA standard C22.3 No.7 and because the reference is a code rule then by extension the standard becomes a compulsory part of the Electrical code for any installation that the other 12 rules do not define. In easy English if the trench is shared with other utilities on the incoming side or to an outbuilding on the consumer side then the other stuff buried must follow the Standard.
Another $175 dollar code document or just stay 300 mm away from water and sewer and gas and don't cross other services except at right angles. Electric crosses lower than sewer since sewer must be graded. Table 53 tells minimum depth of burial.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,453 Are you busy
209,361 Re: Forum
196,636 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3