Can normal and emergency power ckts be share in the same raceway.
I have a 2-section wiremold, 1 for data and 1 for pwr, but the pwr has both normal and emergency ckts.
the emergency ckts are not life safety.
thanks in advance
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Y
Optional (702) Legally required (701)Emergency (700)
read 700.9 (B) , 701.10,& 702.9
700.9(B) - NO
701.10 - Yes
702.9 - Yes
To answer your question you must first determine what your circuits are. Emergency (700) Legally Required ( 701) or Optional ( 702)
Read 700.1 & 700.2 and 701.1 & 701.2 and 702.1 & 702.2