Can normal and emergency power ckts be share in the same raceway.

I have a 2-section wiremold, 1 for data and 1 for pwr, but the pwr has both normal and emergency ckts.

the emergency ckts are not life safety.

thanks in advance
Optional (702) Legally required (701)Emergency (700)

read 700.9 (B) , 701.10,& 702.9

700.9(B) - NO

701.10 - Yes

702.9 - Yes

To answer your question you must first determine what your circuits are. Emergency (700) Legally Required ( 701) or Optional ( 702)
Read 700.1 & 700.2 and 701.1 & 701.2 and 702.1 & 702.2
to determine what you have.