0 members (),
160
guests, and
27
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Jul 2002
Posts: 241
OP
Member
|
There is an outside Air Conditioning compressor for Central Air. The name plate running Amps says 19amps. 30 amp breaker at the Panel. Even though the code says #12 is good for 25 amps, the unit should be wired in #10 wire, right? Is there an exception in the 440 section of the code? As far as I know #12's limit is 20 amps. No exceptions? Thanks - Good Day
|
|
|
|
|
Joined: Jul 2004
Posts: 10,041 Likes: 37
Member
|
If the "19 Amps" is labeled as the "minimum circuit ampacity" or words to that effect. Grab a hold of your hat. You could use #14. (per 310.16, 60 degree column). There was a question on the inspectors test about a 1hp motor on a 120v circuit where the right answer was "40a breaker, 14 ga wire". Strange sounding things happen around motors and HVAC units. The exception is in 240.4(G) (2008 code or in 240.4(D)ex in earlier versions).
Greg Fretwell
|
|
|
|
|
Joined: Jul 2002
Posts: 241
OP
Member
|
I seen 240.4(D)(5), saying 12 AWG Copper - 20 amperes. I thought I had to go with that? Is 240.4(G) only refer to Overcurrent Protection, so I would have to go to a #10? Could I leave #12's? The Electrician already wired the unit with 12's.
|
|
|
|
|
Joined: Jul 2004
Posts: 10,041 Likes: 37
Member
|
It says 240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied. so the whole issue is about overcurrent protection.
Greg Fretwell
|
|
|
|
|
Joined: Jul 2002
Posts: 241
OP
Member
|
Table 310.16 (left side) has the * next to #'s 14, 12, and 10. Does the asterik mean you have to keep #12 at 20 amps?
|
|
|
|
|
Joined: Jul 2004
Posts: 10,041 Likes: 37
Member
|
No that just refers you to 240.4(D) which then further defines the necessary overcurrent protection for small conductors in any use not excepted by 240.4(G) or (E).
Greg Fretwell
|
|
|
|
|
Joined: Jul 2002
Posts: 241
OP
Member
|
Thanks, I'll go through Article 440 parts 3 and 6.
|
|
|
|
|
Joined: Jul 2004
Posts: 10,041 Likes: 37
Member
|
The short answer is the label on the condenser rules. Another interesting read is the U/L marking guide for HVAC equipment. Unfortunately they don't have it online without paying for it.
Greg Fretwell
|
|
|
Posts: 8,450
Joined: July 2002
|
|
|
|
|
|