Laundry room panel calculation #194176 05/14/10 02:01 AM
Joined: May 2010
Posts: 2
K
Kuzn Offline OP
New Member
Hi I need to calculate the electrical panel capacity for the strata laundry room upgrade. Strata plans to have 3 stacked dryers (dryer/dryer) 240V/60Amp - hardwired and 6 washers 120V/15Amp receptacles. Should I calculate it as 100% continuous load (3*60+6*15) =270 Amp.
Can you please remind me what CEC says?
Thank you

Tools for Electricians:
Re: Laundry room panel calculation [Re: Kuzn] #194246 05/18/10 12:21 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
From 8-202 (4) "The ampacity of feeder conductors from a service supplying loads not located in dwelling units shall be not less than the rating of the equipment installed with demand factors as permitted by this code."

So in your case, it is 100%, since you have not listed any electric space heating loads, where you would add them at 75% from 62-116(3).

Re: Laundry room panel calculation [Re: jay8] #194270 05/19/10 01:36 PM
Joined: May 2010
Posts: 2
K
Kuzn Offline OP
New Member
I'm confused with 8-202(3)(d)...power loads not located in dwelling units shell be added with a demand factor of 75%. This panel is for laundry load only, no heating, no lightning.

Thank you

Re: Laundry room panel calculation [Re: Kuzn] #194272 05/19/10 02:56 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
I dont blame you for being confused, but 8-202 (3) refers to the main service feeder calculation while 8-202 (4) refers to just feeders for the house panels.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 8
Popular Topics(Views)
257,934 Are you busy
193,669 Re: Forum
183,284 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3