ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
AreMetal Ladders Ever OK For Electrical Work?
by HotLine1. 01/22/18 07:31 PM
Photocell
by twh. 01/22/18 05:06 PM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 6 guests, and 6 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Laundry room panel calculation #194176
05/14/10 01:01 AM
05/14/10 01:01 AM
K
Kuzn  Offline OP
New Member
Joined: May 2010
Posts: 2
BC Canada
Hi I need to calculate the electrical panel capacity for the strata laundry room upgrade. Strata plans to have 3 stacked dryers (dryer/dryer) 240V/60Amp - hardwired and 6 washers 120V/15Amp receptacles. Should I calculate it as 100% continuous load (3*60+6*15) =270 Amp.
Can you please remind me what CEC says?
Thank you

Tools for Electricians:
Re: Laundry room panel calculation [Re: Kuzn] #194246
05/18/10 11:21 AM
05/18/10 11:21 AM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
From 8-202 (4) "The ampacity of feeder conductors from a service supplying loads not located in dwelling units shall be not less than the rating of the equipment installed with demand factors as permitted by this code."

So in your case, it is 100%, since you have not listed any electric space heating loads, where you would add them at 75% from 62-116(3).

Re: Laundry room panel calculation [Re: jay8] #194270
05/19/10 12:36 PM
05/19/10 12:36 PM
K
Kuzn  Offline OP
New Member
Joined: May 2010
Posts: 2
BC Canada
I'm confused with 8-202(3)(d)...power loads not located in dwelling units shell be added with a demand factor of 75%. This panel is for laundry load only, no heating, no lightning.

Thank you

Re: Laundry room panel calculation [Re: Kuzn] #194272
05/19/10 01:56 PM
05/19/10 01:56 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I dont blame you for being confused, but 8-202 (3) refers to the main service feeder calculation while 8-202 (4) refers to just feeders for the house panels.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,405 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.9583 MB (Peak: 1.0911 MB) Zlib enabled. Server Time: 2018-01-23 11:57:47 UTC