Joined: Feb 2002
Posts: 2,233
H
Member
OK, How about a Jandy (sp?) panel for an outside hot tub? Do you need a full 30" clearance in front of the panelboard? There are several breakers inside ( motor, light, blower, etc) however there are 2 large pumps in front of the panel. You can open the panel door to 90 deg and more, and there is nothing directly in front of the panel, just those 2 motors on the ground right in front. You have to reach over the motors to work on the panel.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Mar 2005
Posts: 212
G
Member
Harold, I've never worked under an AHJ who would let me out of the requirement in the case you cite. It's definitely a "switchboard or panelboard". The pool guys love to take up all the available space when they get there first, but when the inspector won't let anyone in the pool they usually move those pumps. The only thing I've seen get by is obstructions in the space above the panel, especially if it was existing.

Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
I think I would be more concerned about that Jandy panel than a condenser disconnect. You have a lot better chance of a marginally qualified person working on it. Having obstructed work space makes even more likely that "pool boy" will fall into an energized conductor. (maybe wet and barefooted)


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
I have an EC trying to tell me that it is OK to have the pool pumps right in front of the Jandy panelboard, because you can open the panel 90 deg and more, plus you can still work on the breakers/equipment. (You just have to reach over two 2hp pump motors!)

Joined: Mar 2005
Posts: 212
G
Member
Well Harold, it sucks to be wrong, especially when it's going to cost money. But the EC in the case you cite is just wrong. That Jandy panel needs the same clearance as any other.

Joined: Feb 2002
Posts: 2,233
H
Member
I got in touch with the DCA last week and they agreed with my decision and I know that it is tough for the EC, but the pool people should have thought of that before they installed the pumps in front of the panel. I believe the EC was there first, so the pool people should be made to move their equipment.

Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
Harold:
Wasn't the accident where a pool person got electrocuted caused by reaching over a pump to reach a disconnect?

Yes, the motor was not bonded properly as I remember.