ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Questioning the electrical norms
by HotLine1 - 03/04/21 12:35 PM
Lock-down Thread
by gfretwell - 03/03/21 12:38 PM
Northern Tool Recalls Powerhorse Generators
by Admin - 02/25/21 09:49 PM
You will never guess
by gfretwell - 02/25/21 07:48 PM
New in the Gallery:
Facebook follies, bad wiring
FPE in Germany pt.2
Who's Online Now
0 registered members (), 15 guests, and 21 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
blown in insulation with K&T #193758 04/17/10 01:16 PM
Joined: Dec 2005
Posts: 12
O
Oh Well Offline OP
Member
I couldn't find a topic relating to this so here goes. The Ont.electrical does not mention insulating existing walls that have knob and tube wiring. Would this be covered under the building code? I know it's not a good practice but who actually regulates this. Thanks in advance.

Tools for Electricians:
Re: blown in insulation with K&T [Re: Oh Well] #193899 04/27/10 01:23 AM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
You would not find anything in the building code regarding blown in insulation in a cavity where knob and tube exists. But if you wanted to make a case where you wanted to point out it could not be done, that would be an electrical code issue. In this case since knob and tube wiring gives no temperature ratings, you could say it is not then suitable to be enclosed in thermal insulation since it is not marked as such. However I know there are hundreds of homes out there that would have insulated attics with knob and tube, not saying it is right.

Re: blown in insulation with K&T [Re: jay8] #193908 04/27/10 12:44 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
2-124 of the 1986 Canadian electrical code does not prohibit thermal insulation . It states that the insulation must not put any stress on the wire associated with the weight of insulation. Insulation with a mettalic face must be kept 25mm away from K&T.
Loose blown in insulation is OK with any type of wiring method recognized by the code.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,704 Are you busy
209,627 Re: Forum
196,966 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3