blown in insulation with K&T #193758 04/17/10 01:16 PM
Joined: Dec 2005
Posts: 12
O
Oh Well Offline OP
Member
I couldn't find a topic relating to this so here goes. The Ont.electrical does not mention insulating existing walls that have knob and tube wiring. Would this be covered under the building code? I know it's not a good practice but who actually regulates this. Thanks in advance.

Tools for Electricians:
Re: blown in insulation with K&T [Re: Oh Well] #193899 04/27/10 01:23 AM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
You would not find anything in the building code regarding blown in insulation in a cavity where knob and tube exists. But if you wanted to make a case where you wanted to point out it could not be done, that would be an electrical code issue. In this case since knob and tube wiring gives no temperature ratings, you could say it is not then suitable to be enclosed in thermal insulation since it is not marked as such. However I know there are hundreds of homes out there that would have insulated attics with knob and tube, not saying it is right.

Re: blown in insulation with K&T [Re: jay8] #193908 04/27/10 12:44 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
2-124 of the 1986 Canadian electrical code does not prohibit thermal insulation . It states that the insulation must not put any stress on the wire associated with the weight of insulation. Insulation with a mettalic face must be kept 25mm away from K&T.
Loose blown in insulation is OK with any type of wiring method recognized by the code.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
dsk 10
Trumpy 4
Popular Topics(Views)
262,587 Are you busy
197,704 Re: Forum
186,703 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3