L
Member
I am remodeling my kitchen and came across this problem. The wall studding and wall board is used as a chase for a return duct and I would like to put a receptacle in that chase, if I use m/c cable and a metal box can I put this recept. in this chase.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Dec 2000
Posts: 4,294
Member
If I understand you correctly, it's a ducted return running through the chase, and not an actual chase for the handling of environmental air.

Is the receptacle going to be accessible after you're finished?
Will the cord have to run through a hole in the drywall?


.


Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
If this stud bay is the duct I think that you will be sucking dust into the receptacle, eventually packing the enclosure you added.
Think about the case of your PC where the air comes in.


Greg Fretwell
Joined: Nov 2000
Posts: 2,148
R
Member
This would be a 300.22(C) installation. It looks like 300.22(C)(2) would permit this.


Don(resqcapt19)
Joined: Feb 2008
Posts: 165
R
Member
Originally Posted by resqcapt19
This would be a 300.22(C) installation. It looks like 300.22(C)(2) would permit this.
This is correct we have had to do this where return air space and receptacles were in the same spot

Joined: Feb 2006
Posts: 78
L
Member
What I'M saying is in the basement they panned off two bays for the return then over the panning there is a partion wall that is just studded out and drywall with a register grill, the bottom plate is cut out for the return air to flow down to the panned area I would like to put a recept in the wall chase that is really a return duct. The wiring will be running thru the partion wall and stopping in the wall chase return with a recept using m/c cable and a metal box cancealed in the wall.

Joined: Feb 2008
Posts: 165
R
Member
you are good to go.The method is approved see 300.22(C)(2)

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Mar 2005
Posts: 399
A
Member
Wiring can pass through (across) the stud space used as a return air (duct). A box and receptacle in that space would be a violation.
If the receptacle will be mounted above the register grill, a piece of wood across the space would effectively seperate the return air (duct) part of the stud space from the part with the receptacle.


Alan--
If it was easy, anyone could do it.
Joined: Feb 2008
Posts: 165
R
Member
Originally Posted by Alan Nadon
Wiring can pass through (across) the stud space used as a return air (duct). A box and receptacle in that space would be a violation.
If the receptacle will be mounted above the register grill, a piece of wood across the space would effectively seperate the return air (duct) part of the stud space from the part with the receptacle.
Whats your code reference

Joined: Feb 2006
Posts: 78
L
Member
Thanks for everyones reply.