wiring in return air #192499
02/16/10 11:27 AM
02/16/10 11:27 AM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
I am remodeling my kitchen and came across this problem. The wall studding and wall board is used as a chase for a return duct and I would like to put a receptacle in that chase, if I use m/c cable and a metal box can I put this recept. in this chase.

2017 / 2014 NEC & Related Books and Study Guides
Re: wiring in return air [Re: lite bulb] #192500
02/16/10 12:05 PM
02/16/10 12:05 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,266
Fullerton, CA USA
If I understand you correctly, it's a ducted return running through the chase, and not an actual chase for the handling of environmental air.

Is the receptacle going to be accessible after you're finished?
Will the cord have to run through a hole in the drywall?


.


Re: wiring in return air [Re: electure] #192504
02/16/10 02:35 PM
02/16/10 02:35 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,225
Estero,Fl,usa
If this stud bay is the duct I think that you will be sucking dust into the receptacle, eventually packing the enclosure you added.
Think about the case of your PC where the air comes in.


Greg Fretwell
Re: wiring in return air [Re: gfretwell] #192524
02/16/10 10:43 PM
02/16/10 10:43 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
This would be a 300.22(C) installation. It looks like 300.22(C)(2) would permit this.


Don(resqcapt19)
Re: wiring in return air [Re: resqcapt19] #192526
02/16/10 11:31 PM
02/16/10 11:31 PM
R
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
Originally Posted by resqcapt19
This would be a 300.22(C) installation. It looks like 300.22(C)(2) would permit this.
This is correct we have had to do this where return air space and receptacles were in the same spot

Re: wiring in return air [Re: electure] #192532
02/17/10 12:14 AM
02/17/10 12:14 AM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
What I'M saying is in the basement they panned off two bays for the return then over the panning there is a partion wall that is just studded out and drywall with a register grill, the bottom plate is cut out for the return air to flow down to the panned area I would like to put a recept in the wall chase that is really a return duct. The wiring will be running thru the partion wall and stopping in the wall chase return with a recept using m/c cable and a metal box cancealed in the wall.

Re: wiring in return air [Re: lite bulb] #192537
02/17/10 12:36 AM
02/17/10 12:36 AM
R
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
you are good to go.The method is approved see 300.22(C)(2)

Re: wiring in return air [Re: Rewire] #192553
02/17/10 02:28 PM
02/17/10 02:28 PM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
Wiring can pass through (across) the stud space used as a return air (duct). A box and receptacle in that space would be a violation.
If the receptacle will be mounted above the register grill, a piece of wood across the space would effectively seperate the return air (duct) part of the stud space from the part with the receptacle.


Alan--
If it was easy, anyone could do it.
Re: wiring in return air [Re: Alan Nadon] #192564
02/17/10 09:17 PM
02/17/10 09:17 PM
R
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
Originally Posted by Alan Nadon
Wiring can pass through (across) the stud space used as a return air (duct). A box and receptacle in that space would be a violation.
If the receptacle will be mounted above the register grill, a piece of wood across the space would effectively seperate the return air (duct) part of the stud space from the part with the receptacle.
Whats your code reference

Re: wiring in return air [Re: Rewire] #192568
02/17/10 10:37 PM
02/17/10 10:37 PM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Thanks for everyones reply.

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,903 Are you busy
184,257 Re: Forum
173,496 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 16 (0.004s) Memory: 1.0260 MB (Peak: 1.2063 MB) Zlib enabled. Server Time: 2018-05-25 11:00:52 UTC