ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
turning down possible problem customer
by HotLine1. 05/21/18 07:53 AM
480 Delta
by sparkyinak. 05/20/18 09:33 PM
Furnace igniter leaking noise to stereo
by sparkyinak. 05/20/18 07:20 PM
electircal ageing test on IPC
by HotLine1. 05/14/18 09:42 AM
What estimating software do you recommend?
by wattsittoyou. 05/14/18 06:28 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
2 registered members (Tjia1981, ghost307), 9 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Old Coleman Powermate Generator question #192170
01/30/10 02:43 PM
01/30/10 02:43 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
I have acquired an older Coleman Powermate PM0545202.01 5Kw generator.

It has 120/240 volt receptacles: 2 NEMA 5-15R, and 1 6-15R, but I can not seem to find a schematic for it. I am quite surprised that the 240V receptacle is 15A...

My question is, can I get 240V with a neutral out of it, or are the windings completely separate?

Thanks in advance.

Grov

Work Gear for Electricians and the Trades
Re: Old Coleman Powermate Generator question [Re: Grover] #192179
01/30/10 11:03 PM
01/30/10 11:03 PM
D
davemica  Offline
Member
Joined: Oct 2005
Posts: 12
florida
I had one of those. Mine did not have a neutral, the 240 was straight 240.

Re: Old Coleman Powermate Generator question [Re: davemica] #192183
01/31/10 11:17 AM
01/31/10 11:17 AM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
that's what I was afraid of.... Do you happen to have a schematic of the windings?

Re: Old Coleman Powermate Generator question [Re: Grover] #192185
01/31/10 02:48 PM
01/31/10 02:48 PM
D
davemica  Offline
Member
Joined: Oct 2005
Posts: 12
florida
I don't have a schematic.

Re: Old Coleman Powermate Generator question [Re: davemica] #192187
01/31/10 03:41 PM
01/31/10 03:41 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
I think if you have 120 and 240 it must have a shared neutral unless there are 2 completely separate windings and a meter should show you that (ohm scale). My bet is you have 120-0-120 just like your house. Have you tried measuring between the hots of the two 5-15s? Is that is 240? Is there continuity between those neutrals? (more evidence that it is likely center tapped).
The open question is if the neutral is bonded.


Greg Fretwell
Re: Old Coleman Powermate Generator question [Re: gfretwell] #192201
02/01/10 12:57 PM
02/01/10 12:57 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
Thanks Greg!

I'll check later today, but we're thinking along the same lines. Gotta wait 'till the temp gets up to at least 20!

Re: Old Coleman Powermate Generator question [Re: Grover] #192236
02/02/10 08:31 PM
02/02/10 08:31 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
I used to repair those generators. No, I do not have any schematics. However Century Powermate built most of the store branded equipment. Therefore Snap-on, Sears, Montgomery-Wards, Coleman, Schauer, any of the automotive part store chains branded generators, welders, battery chargers, etc are all built by Century Powermate. The only differences are typically sheet metal and paint.

If you can find a schematic for a similar sized private label brand generator, it will probably be the same schematic.

Larry C


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,851 Are you busy
184,206 Re: Forum
173,447 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 0.9850 MB (Peak: 1.1416 MB) Zlib enabled. Server Time: 2018-05-21 13:14:18 UTC