Hi— Found on the roof of a local starbux; it all sits on a TB supported by a piece of ½-inch EMT...
They look like a pair of 500W quartz-halogen fixtures.
How would you "bring this up to code"? —busbar
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 2
Cat Servant Member
|
Just where is the violation?
OK, maybe there's a fill issue in the conduit body ... but using a Bell box would not change the support issue one bit.
The fixtures arefairlylightweight, and the length of the mast isn't very much.
Cheap? Schlock? Absolutely- but I think it meets code.
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
It's a violation of the support required by 314.23(F).
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 2
Cat Servant Member
|
Good catch, Electure! So.... rigidis OK for this use, but not EMT.
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
Is there anough room inside the T to legally make up the splices?
Ghost307
|
|
|
|
Joined: Mar 2008
Posts: 76
Member
|
I agree ghost307, that's a good question.
I have a sense of adventure, I just keep it leashed with common sense.
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
As long as you don't exceed the fill percentage of the fitting, you can make splices in them. I can't recall the Code section offhand though...
I have seen splices in T-fittings before, they seem to fit ok without too much drama.
Stupid should be painful.
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
some conduit bodies are approved for a splice some are not and I don't know the differences.
Last edited by mikesh; 04/21/09 06:56 PM. Reason: spelling
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
If they have the CU IN stamped inside the TB conduit body then yeah it can be used for splices otherwise no it can not be used for splices but I know some guys do used the oversied TB bodies for it and install the reduced bushing in there to make room for splices.
Merci,Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
I've used the 'over size' method a few times.mainly for parking garage light retros'
|
|
|