Hi Guys, I am doing a 600a 1phase service and I was going to use 350kmcm in parallel, my friend from a diffrent firm is telling me they used 300kmcm for one just recently. Now I am second guessing myself, so I am turning to you all.
Ob
Choose your customers, don't let them choose you.
|
|
|
Re: Wire for 600A 1Phase service
[Re: Obsaleet]
#185667
03/23/09 10:08 PM
|
Joined: Apr 2002
Posts: 7,237
Member
|
300KCMil Copper, 75 degree col is 285 amps,Based on 240.4 (B)parallel is 570 amps, next higher available is 600 amps.
300's work.
John
|
|
|
Re: Wire for 600A 1Phase service
[Re: Obsaleet]
#185668
03/23/09 10:14 PM
|
Joined: Mar 2003
Posts: 849
Member
|
If in two seperate conduits 300 kcmil is good for 285 amps at 75c. see 240.4 (b) (800 amps or less next higest breaker size) . 240.6 300 next breaker size is 600. 285 plus 285 = 570 if in one single conduit see table 310.15(B)(2)(a) 4-6 80% 570x80%=456 next higest per 240.6= 500amp. Same Conduit would require 400 Kcmil 335x2= 670 x 80%= 536 . 240.6 next higest 600 This is with 3 wires in conduit single phase. Or 6 wires in conduit single phase.
|
|
|
|
|