Wire for 600A 1Phase service #185665
03/23/09 09:22 PM
03/23/09 09:22 PM
Obsaleet  Offline OP
Member
Joined: Apr 2003
Posts: 362
Pa
Hi Guys, I am doing a 600a 1phase service and I was going to use 350kmcm in parallel, my friend from a diffrent firm is telling me they used 300kmcm for one just recently. Now I am second guessing myself, so I am turning to you all.


Ob


Choose your customers, don't let them choose you.
Work Gear for Electricians and the Trades
Re: Wire for 600A 1Phase service [Re: Obsaleet] #185667
03/23/09 10:08 PM
03/23/09 10:08 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,084
Brick, NJ USA
300KCMil Copper, 75 degree col is 285 amps,Based on 240.4 (B)parallel is 570 amps, next higher available is 600 amps.

300's work.


John
Re: Wire for 600A 1Phase service [Re: Obsaleet] #185668
03/23/09 10:14 PM
03/23/09 10:14 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
If in two seperate conduits 300 kcmil is good for 285 amps at 75c. see 240.4 (b) (800 amps or less next higest breaker size) .
240.6 300 next breaker size is 600.
285 plus 285 = 570
if in one single conduit see table 310.15(B)(2)(a)
4-6 80%
570x80%=456 next higest per 240.6= 500amp.
Same Conduit would require 400 Kcmil
335x2= 670 x 80%= 536 . 240.6 next higest 600
This is with 3 wires in conduit single phase. Or
6 wires in conduit single phase.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,152
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,517 Are you busy
190,759 Re: Forum
180,477 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.9519 MB (Peak: 1.0774 MB) Zlib enabled. Server Time: 2019-04-21 22:20:30 UTC