ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 8
Recent Posts
OD of Alum and Copper
by HotLine1. 08/23/17 07:30 PM
Grid problem??
by annemarie1. 08/21/17 01:10 PM
Bathroom electrical
by doc. 08/19/17 06:53 AM
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,156 Are you busy
175,803 Re: Forum
167,965 Need opinion
Who's Online Now
0 registered members (), 60 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#185665 - 03/23/09 09:22 PM Wire for 600A 1Phase service  
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
Hi Guys, I am doing a 600a 1phase service and I was going to use 350kmcm in parallel, my friend from a diffrent firm is telling me they used 300kmcm for one just recently. Now I am second guessing myself, so I am turning to you all.


Ob


Choose your customers, don't let them choose you.

Work Gear for Electricians and the Trades

#185667 - 03/23/09 10:08 PM Re: Wire for 600A 1Phase service [Re: Obsaleet]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,859
Brick, NJ USA
300KCMil Copper, 75 degree col is 285 amps,Based on 240.4 (B)parallel is 570 amps, next higher available is 600 amps.

300's work.


John

#185668 - 03/23/09 10:14 PM Re: Wire for 600A 1Phase service [Re: Obsaleet]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 825
Michigan
If in two seperate conduits 300 kcmil is good for 285 amps at 75c. see 240.4 (b) (800 amps or less next higest breaker size) .
240.6 300 next breaker size is 600.
285 plus 285 = 570
if in one single conduit see table 310.15(B)(2)(a)
4-6 80%
570x80%=456 next higest per 240.6= 500amp.
Same Conduit would require 400 Kcmil
335x2= 670 x 80%= 536 . 240.6 next higest 600
This is with 3 wires in conduit single phase. Or
6 wires in conduit single phase.



Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,260
Joined: December 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.002s) Memory: 0.7527 MB (Peak: 0.8766 MB) Zlib enabled. Server Time: 2017-08-24 02:59:29 UTC