I found this photo on the internet and am wondering why 2 things.
1. Why is there only 2 CT's, with the B phase unmetered? 2. If the color code is right, this is a 208Y/120V 4 wire system. Where is the grounded(neutral) conductor? Isn't this a violation of 250.24(C)? I have never seen a CT cabinet that didnt have a CT for each phase. Maybe someone could steer me in the right direction. Thanks, Gary Edited to add code section
A Delta service is metered with two CTs. The service being either corner grounded or not, does not change the metering setup. The picture also shows a three phase, four wire meter socket. I think either the CT configuration is wrong or the socket is wrong.
The only other possiblty when you see two CT's there it possbilty that is used for electric motor load only { I did see it in few place like that however POCO don't like it much }
Merci,Marc
P.S. look like 60 a 240 or 208 volt otherwise 480 v 30 amp due the conductor size looks pretty small.
Last edited by frenchelectrican; 02/07/0906:37 AM. Reason: add more info
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
It looks like an overkill to me for CT metering. That size cable looks like 16 or 25 mm˛ and the power usage could have been metered directly with a whole current meter.
This CT set up adds hugely to the overall installation costs.