CT cabinet with only 2 CT's in it #184299
02/06/09 05:46 PM
02/06/09 05:46 PM
T
trekkie76  Offline OP
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
[Linked Image]

I found this photo on the internet and am wondering why 2 things.

1. Why is there only 2 CT's, with the B phase unmetered?
2. If the color code is right, this is a 208Y/120V 4 wire system. Where is the grounded(neutral) conductor? Isn't this a violation of 250.24(C)?
I have never seen a CT cabinet that didnt have a CT for each phase. Maybe someone could steer me in the right direction.
Thanks,
Gary
Edited to add code section

Last edited by trekkie76; 02/06/09 05:51 PM.
Tools for Electricians:
Re: CT cabinet with only 2 CT's in it [Re: trekkie76] #184301
02/06/09 06:53 PM
02/06/09 06:53 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,001
Brick, NJ USA
Disregarding the 'color code'.....600 volt fuses in disco, looks like 3 phase, 3 wire (delta) 480 volt service.

I only came accross this twice, a long time ago; industrial


John
Re: CT cabinet with only 2 CT's in it [Re: trekkie76] #184302
02/06/09 07:24 PM
02/06/09 07:24 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Corner grounded Delta system?

Larry C

Re: CT cabinet with only 2 CT's in it [Re: LarryC] #184306
02/06/09 08:45 PM
02/06/09 08:45 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
Shouldn't that CT enclosure and the meter base enclosure also have a ground wire attached to them and run back to that ground wire in the Disconnect?

Re: CT cabinet with only 2 CT's in it [Re: Trumpy] #184307
02/06/09 09:25 PM
02/06/09 09:25 PM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 794
Chicago, Il.
Whether corner grounded or not, don't 2 CTs give you all you need on a delta??? Not true with a wye.
Joe

Re: CT cabinet with only 2 CT's in it [Re: JoeTestingEngr] #184309
02/06/09 09:59 PM
02/06/09 09:59 PM
A
ameterguy  Offline
Member
Joined: May 2002
Posts: 30
Mass
A Delta service is metered with two CTs. The service being either corner grounded or not, does not change the metering setup.
The picture also shows a three phase, four wire meter socket. I think either the CT configuration is wrong or the socket is wrong.

Re: CT cabinet with only 2 CT's in it [Re: ameterguy] #184326
02/07/09 07:34 AM
02/07/09 07:34 AM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
The only other possiblty when you see two CT's there it possbilty that is used for electric motor load only { I did see it in few place like that however POCO don't like it much }

Merci,Marc

P.S. look like 60 a 240 or 208 volt otherwise 480 v 30 amp due the conductor size looks pretty small.

Last edited by frenchelectrican; 02/07/09 07:37 AM. Reason: add more info

Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: CT cabinet with only 2 CT's in it [Re: frenchelectrican] #184328
02/07/09 01:52 PM
02/07/09 01:52 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,001
Brick, NJ USA
Looks like max 30 amp fused disco at 480/600 volt as I look again.

POCO here supplies CT's and meter pan, and installs wiring from CT's to pan.



John
Re: CT cabinet with only 2 CT's in it [Re: HotLine1] #184340
02/07/09 05:08 PM
02/07/09 05:08 PM
R
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 856
Titirangi, Akld, New Zealand
It looks like an overkill to me for CT metering.
That size cable looks like 16 or 25 mm and the power usage could have been metered directly with a whole current meter.

This CT set up adds hugely to the overall installation costs.


The product of rotation, excitation and flux produces electricty.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,670 Are you busy
186,403 Re: Forum
175,893 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.003s) Memory: 1.0032 MB (Peak: 1.1714 MB) Zlib enabled. Server Time: 2018-08-21 09:56:54 UTC