CT cabinet with only 2 CT's in it #184299 02/06/09 04:46 PM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline OP
Member
[Linked Image from electrical-photos.com]

I found this photo on the internet and am wondering why 2 things.

1. Why is there only 2 CT's, with the B phase unmetered?
2. If the color code is right, this is a 208Y/120V 4 wire system. Where is the grounded(neutral) conductor? Isn't this a violation of 250.24(C)?
I have never seen a CT cabinet that didnt have a CT for each phase. Maybe someone could steer me in the right direction.
Thanks,
Gary
Edited to add code section

Last edited by trekkie76; 02/06/09 04:51 PM.
Tools for Electricians:
Re: CT cabinet with only 2 CT's in it [Re: trekkie76] #184301 02/06/09 05:53 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
Disregarding the 'color code'.....600 volt fuses in disco, looks like 3 phase, 3 wire (delta) 480 volt service.

I only came accross this twice, a long time ago; industrial


John
Re: CT cabinet with only 2 CT's in it [Re: trekkie76] #184302 02/06/09 06:24 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
Corner grounded Delta system?

Larry C

Re: CT cabinet with only 2 CT's in it [Re: LarryC] #184306 02/06/09 07:45 PM
Joined: Jul 2002
Posts: 8,379
Trumpy Offline
Member
Shouldn't that CT enclosure and the meter base enclosure also have a ground wire attached to them and run back to that ground wire in the Disconnect?

Re: CT cabinet with only 2 CT's in it [Re: Trumpy] #184307 02/06/09 08:25 PM
Joined: Nov 2005
Posts: 823
J
JoeTestingEngr Offline
Member
Whether corner grounded or not, don't 2 CTs give you all you need on a delta??? Not true with a wye.
Joe

Re: CT cabinet with only 2 CT's in it [Re: JoeTestingEngr] #184309 02/06/09 08:59 PM
Joined: May 2002
Posts: 30
A
ameterguy Offline
Member
A Delta service is metered with two CTs. The service being either corner grounded or not, does not change the metering setup.
The picture also shows a three phase, four wire meter socket. I think either the CT configuration is wrong or the socket is wrong.

Re: CT cabinet with only 2 CT's in it [Re: ameterguy] #184326 02/07/09 06:34 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
The only other possiblty when you see two CT's there it possbilty that is used for electric motor load only { I did see it in few place like that however POCO don't like it much }

Merci,Marc

P.S. look like 60 a 240 or 208 volt otherwise 480 v 30 amp due the conductor size looks pretty small.

Last edited by frenchelectrican; 02/07/09 06:37 AM. Reason: add more info

Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: CT cabinet with only 2 CT's in it [Re: frenchelectrican] #184328 02/07/09 12:52 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
Looks like max 30 amp fused disco at 480/600 volt as I look again.

POCO here supplies CT's and meter pan, and installs wiring from CT's to pan.



John
Re: CT cabinet with only 2 CT's in it [Re: HotLine1] #184340 02/07/09 04:08 PM
Joined: Dec 2005
Posts: 860
R
RODALCO Offline
Member
It looks like an overkill to me for CT metering.
That size cable looks like 16 or 25 mm˛ and the power usage could have been metered directly with a whole current meter.

This CT set up adds hugely to the overall installation costs.


The product of rotation, excitation and flux produces electricty.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,352 Are you busy
209,224 Re: Forum
196,526 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3