Star Star configuration #183265
01/01/09 09:22 PM
01/01/09 09:22 PM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
Hi all,
I have recently been working on replacing a defective 690v 3 Phase induction motor driving a cooling fan,when i inspected the name plate it has a star configuration for slow speed and a star star configuraton for high speed.The motor has six terminal terminations (not including earth conductors).
When looking at the wiring configuration to the fan its as follows;
slow speed terminals 1,2 and 3 are used for 3 phase electrical supply.
High speed consists of the supply for 1,2 and 3 being disconnected from the incomming supply and then all joined together via little jumper loops in a contactor,terminals 4,5 and 6 then supplies the motor.

Has anyone ever heard or worked with such a configuration?Does this configuration just double up the three phase field windings in star (like the name suggests), producing more electromagnetic force for the stator to react upon?

Where i work has the same wiring set up for other motors and pumps,any help on this matter would much appreciated!

James

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: Star Star configuration [Re: james S] #183292
01/02/09 09:09 PM
01/02/09 09:09 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
James:
You may want to e-mail Pauluk and see if he can help you.

Im going to move this thread to the non-US area Sat. AM



John
Re: Star Star configuration [Re: HotLine1] #183295
01/02/09 10:31 PM
01/02/09 10:31 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,247
SI,New Zealand
Gidday James,
It sounds like what you are describing is a motor meant for a Star-Delta starter.
Star-Star (or Double Star) is often another term for Delta configuration.

690V sounds like a strange voltage to be supplying to a motor that drives a fan.

Hope this helps.

Re: Star Star configuration [Re: Trumpy] #183303
01/03/09 09:55 AM
01/03/09 09:55 AM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
whoops sorry HOTLINE 1.

Hi Trumpy,
my situation is that im working on Danish wind turbines that are situated off the west coast of England which explains the Danish 690v.(Its prob so tney can use there own voltage rated components i.e motors,pumps etc.)

I spoke to a Danish engineer about this and he explained the best he could in English which is all the info in the first post,he told me off for saying it was star-delta config.

On the name plate it has a pic of a star config for slow speed and two star symbols next to each other for the high speed ratings.No Delta config in sight!

Re: Star Star configuration [Re: james S] #183304
01/03/09 10:19 AM
01/03/09 10:19 AM
W
Wolfgang  Offline
Member
Joined: Sep 2005
Posts: 153
the very West of Germany
Sounds like a "Dahlander" config, sorry it's probably not a simple star-delta motor.

Go to http://www.moeller.net/en/support/wiring_manual.jsp

Download chapter 8 "All about motors", look at pages around 54 and try to figure which fits best, then come back to the forum.

Re: Star Star configuration [Re: Wolfgang] #183305
01/03/09 10:36 AM
01/03/09 10:36 AM
W
Wolfgang  Offline
Member
Joined: Sep 2005
Posts: 153
the very West of Germany
With the information 2 speeds, fan function and star - double star I suppose you got a motor with a reversible tapped winding what we call a "Dahlander motor" on the continent. Then the second sketch from the left on page 8-54 should fit.

In case the speed ratio is not equal 1:2, I missed it and need more input.

Re: Star Star configuration [Re: Wolfgang] #183306
01/03/09 11:58 AM
01/03/09 11:58 AM
W
Wolfgang  Offline
Member
Joined: Sep 2005
Posts: 153
the very West of Germany
Furthermore 690V is root3 *400V.
For star delta starters you mandatorily use a 690/400 motor, so this is sort of an absolute European standard, but usually in delta config. In an industrial context 690V 3ph isn't uncommon however. and it saves weight which might help on high poles, doesn't it.

Re: Star Star configuration [Re: Wolfgang] #183310
01/03/09 03:21 PM
01/03/09 03:21 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
First, Thank you to whoever 'moved' this thread.
I thought this was the right area.....and I guess I was right!

This site never ceases to amaze me!!


John
Re: Star Star configuration [Re: HotLine1] #183314
01/03/09 08:29 PM
01/03/09 08:29 PM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
Hotline 1,
it will never happen again please forgive me for my actions!


Hi Wolfgang,
your link provided me with the correct configuration and yes it was the second sketch from the left on page 54,even the the terminal numbers/letters tally up with what i have.
I suppose my assumption that the phase windings are doubled up in star was correct,was just a little confused with this arrangement initialy.
Thanks again Wolfgang for the excellant link and your input!

James


Re: Star Star configuration [Re: james S] #183318
01/04/09 12:20 PM
01/04/09 12:20 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
JamesS:
No need for any apology of any type at all!
We are all here to help each other!
Take care


John
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,377 Are you busy
187,308 Re: Forum
176,651 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 16 (0.004s) Memory: 1.0265 MB (Peak: 1.2076 MB) Zlib enabled. Server Time: 2018-09-22 16:55:00 UTC