Posted By: james S Star Star configuration - 01/02/09 01:22 AM
Hi all,
I have recently been working on replacing a defective 690v 3 Phase induction motor driving a cooling fan,when i inspected the name plate it has a star configuration for slow speed and a star star configuraton for high speed.The motor has six terminal terminations (not including earth conductors).
When looking at the wiring configuration to the fan its as follows;
slow speed terminals 1,2 and 3 are used for 3 phase electrical supply.
High speed consists of the supply for 1,2 and 3 being disconnected from the incomming supply and then all joined together via little jumper loops in a contactor,terminals 4,5 and 6 then supplies the motor.

Has anyone ever heard or worked with such a configuration?Does this configuration just double up the three phase field windings in star (like the name suggests), producing more electromagnetic force for the stator to react upon?

Where i work has the same wiring set up for other motors and pumps,any help on this matter would much appreciated!

James
Posted By: HotLine1 Re: Star Star configuration - 01/03/09 01:09 AM
James:
You may want to e-mail Pauluk and see if he can help you.

Im going to move this thread to the non-US area Sat. AM

Posted By: Trumpy Re: Star Star configuration - 01/03/09 02:31 AM
Gidday James,
It sounds like what you are describing is a motor meant for a Star-Delta starter.
Star-Star (or Double Star) is often another term for Delta configuration.

690V sounds like a strange voltage to be supplying to a motor that drives a fan.

Hope this helps.
Posted By: james S Re: Star Star configuration - 01/03/09 01:55 PM
whoops sorry HOTLINE 1.

Hi Trumpy,
my situation is that im working on Danish wind turbines that are situated off the west coast of England which explains the Danish 690v.(Its prob so tney can use there own voltage rated components i.e motors,pumps etc.)

I spoke to a Danish engineer about this and he explained the best he could in English which is all the info in the first post,he told me off for saying it was star-delta config.

On the name plate it has a pic of a star config for slow speed and two star symbols next to each other for the high speed ratings.No Delta config in sight!
Posted By: Wolfgang Re: Star Star configuration - 01/03/09 02:19 PM
Sounds like a "Dahlander" config, sorry it's probably not a simple star-delta motor.

Go to http://www.moeller.net/en/support/wiring_manual.jsp

Download chapter 8 "All about motors", look at pages around 54 and try to figure which fits best, then come back to the forum.
Posted By: Wolfgang Re: Star Star configuration - 01/03/09 02:36 PM
With the information 2 speeds, fan function and star - double star I suppose you got a motor with a reversible tapped winding what we call a "Dahlander motor" on the continent. Then the second sketch from the left on page 8-54 should fit.

In case the speed ratio is not equal 1:2, I missed it and need more input.
Posted By: Wolfgang Re: Star Star configuration - 01/03/09 03:58 PM
Furthermore 690V is root3 *400V.
For star delta starters you mandatorily use a 690/400 motor, so this is sort of an absolute European standard, but usually in delta config. In an industrial context 690V 3ph isn't uncommon however. and it saves weight which might help on high poles, doesn't it.
Posted By: HotLine1 Re: Star Star configuration - 01/03/09 07:21 PM
First, Thank you to whoever 'moved' this thread.
I thought this was the right area.....and I guess I was right!

This site never ceases to amaze me!!
Posted By: james S Re: Star Star configuration - 01/04/09 12:29 AM
Hotline 1,
it will never happen again please forgive me for my actions!


Hi Wolfgang,
your link provided me with the correct configuration and yes it was the second sketch from the left on page 54,even the the terminal numbers/letters tally up with what i have.
I suppose my assumption that the phase windings are doubled up in star was correct,was just a little confused with this arrangement initialy.
Thanks again Wolfgang for the excellant link and your input!

James

Posted By: HotLine1 Re: Star Star configuration - 01/04/09 04:20 PM
JamesS:
No need for any apology of any type at all!
We are all here to help each other!
Take care
Posted By: RODALCO Re: Star Star configuration - 01/04/09 08:59 PM
Usually star-delta is used to start high inertia loads and to minimise the inrush current on the supply.

Mike, (Trumpy) We use 690 Volts 3 Phase in the steelmill.

Cheers, Raymond