Shared neutral and 2 GFI circuits #181371 10/05/08 09:37 PM
Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
Can I run 12/3 across a garage, overhead to a basement, and then use this shared neutral to feed 2 GFI proctected dircuits? Pigtail the neutral to go to each separate circuit - each having 2-3 outlets - unknown and variable loads - depending on homeowner.

Breaker will be a 2 pole 20 - yoked - common trip.

Each GFI will compare incoming - red or black - with neutral, and will be independant of the load on the other red or black feed. Right?

So if the load on the black is 6A and the load on the red is 10A what happens? In this case, does the GFI device look only "downstream", or does it look "upstream" as well - that is, does it see the imbalance at the pigtail, or only on the load side of the device?

Or do I need a 2 pole GFI breaker?

Thanks!

Grov

Work Gear for Electricians and the Trades
Re: Shared neutral and 2 GFI circuits [Re: Grover] #181373 10/05/08 11:22 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Online Content
Member
A gfci does not look at anything on the line side of the device. As long as you split out your multiwire before you feed the GFCIs you will be fine


Greg Fretwell
Re: Shared neutral and 2 GFI circuits [Re: gfretwell] #181378 10/06/08 06:18 AM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline
Member
2 pole GFCI breaker will not work in that application, stick with the receptacles they will work for you.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Shared neutral and 2 GFI circuits [Re: wire_twister] #181379 10/06/08 06:56 AM
Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
Thanks guys!

Grov

Re: Shared neutral and 2 GFI circuits [Re: Grover] #181380 10/06/08 08:24 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Actually, a 2-pole GFCI would work in your case, but there is no need to use one. Your GFCI receptacles idea is just fine.

GFCI's simply look at the total amount of current that flows out of their load terminals and compare it to the total amount that flows back in.

Re: Shared neutral and 2 GFI circuits [Re: JBD] #181475 10/11/08 04:51 AM
Joined: Dec 2001
Posts: 2,491
T
Texas_Ranger Offline
Member
After all your 120/240 3 wire feeder is just like what feeds your main panel, so what should be the problem?


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,442 Are you busy
209,344 Re: Forum
196,623 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3