Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
Can I run 12/3 across a garage, overhead to a basement, and then use this shared neutral to feed 2 GFI proctected dircuits? Pigtail the neutral to go to each separate circuit - each having 2-3 outlets - unknown and variable loads - depending on homeowner.

Breaker will be a 2 pole 20 - yoked - common trip.

Each GFI will compare incoming - red or black - with neutral, and will be independant of the load on the other red or black feed. Right?

So if the load on the black is 6A and the load on the red is 10A what happens? In this case, does the GFI device look only "downstream", or does it look "upstream" as well - that is, does it see the imbalance at the pigtail, or only on the load side of the device?

Or do I need a 2 pole GFI breaker?

Thanks!

Grov

Joined: Jul 2004
Posts: 9,662
Likes: 4
G
Member
A gfci does not look at anything on the line side of the device. As long as you split out your multiwire before you feed the GFCIs you will be fine


Greg Fretwell
Joined: Jul 2007
Posts: 265
W
Member
2 pole GFCI breaker will not work in that application, stick with the receptacles they will work for you.


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Jan 2005
Posts: 109
Grover Offline OP
Member
Thanks guys!

Grov

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Actually, a 2-pole GFCI would work in your case, but there is no need to use one. Your GFCI receptacles idea is just fine.

GFCI's simply look at the total amount of current that flows out of their load terminals and compare it to the total amount that flows back in.

Joined: Dec 2001
Posts: 2,492
T
Member
After all your 120/240 3 wire feeder is just like what feeds your main panel, so what should be the problem?


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
282,903 Are you busy
216,666 Re: Forum
203,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5